Contractor Talk - Professional Construction and Remodeling Forum banner

subpanel working clearance

4 reading
19K views 14 replies 11 participants last post by  Tinstaafl  
#1 ·
I have a subpanel installed in a laundry room. The wall the panel is installed on is only 24" wide from side to side with a door to the left of it. Would this meet the clearance requirements?
 

Attachments

#3 ·
I'm guessing this is not a permitted job? A quick call to your building department would help.

Also, I have the two main inspectors cell numbers. If I can't get in touch with my building dept I call them. They are pretty awesome guys always willing to help out.
 
#4 ·
E3405.1 Working space and clearances. Sufficient access and working space shall be provided and maintained around all electrical equipment to permit ready and safe operation and maintenance of such equipment in accordance with this section and Figure E3405.1.


Image



For SI: 1 inch = 25.4 mm, 1 foot = 304.8 mm.

a. Equipment, piping and ducts foreign to the electrical installation shall not be placed in the shaded areas extending from the floor to a height of 6 feet above the panelboard enclosure, or to the structural ceiling, whichever is lower.

b. The working space shall be clear and unobstructed from the floor to a height of 6.5 feet.

c. The working space shall not be designated for storage.

d. Panelboards, service equipment and similar enclosures shall not be located in bathrooms, toilet rooms, clothes closets or over the steps of a stairway.

e. Such work spaces shall be provided with artificial lighting where located indoors.

FIGURE E3405.1a, b, c, d, e WORKING SPACE AND CLEARANCES

E3405.2 Working clearances for energized equipment and panelboards. Except as otherwise specified in Chapters 34 through 43, the dimension of the working space in the direction of access to panelboards and live parts likely to require examination, adjustment, servicing or maintenance while energized shall be not less than 36 inches (914 mm) in depth. Distances shall be measured from the energized parts where such parts are exposed or from the enclosure front or opening where such parts are enclosed. In addition to the 36-inch dimension (914 mm), the work space shall not be less than 30 inches (762 mm) wide in front of the electrical equipment and not less than the width of such equipment. The work space shall be clear and shall extend from the floor or platform to a height of 6.5 feet (1981 mm). In all cases, the work space shall allow at least a 90-degree (1.57 rad) opening of equipment doors or hinged panels. Equipment associated with the electrical installation located above or below the electrical equipment shall be permitted to extend not more than 6 inches (152 mm) beyond the front of the electrical equipment.

E3405.3 Dedicated panelboard space. The space equal to the width and depth of the panelboard and extending from the floor to a height of 6 feet (1829 mm) above the panelboard, or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. Piping, ducts, leak protection apparatus and other equipment foreign to the electrical installation shall not be installed in such dedicated space. The area above the dedicated space shall be permitted to contain foreign systems, provided that protection is installed to avoid damage to the electrical equipment from condensation, leaks and breaks in such foreign systems (see Figure E3405.1).

Exception: Suspended ceilings with removable panels shall be permitted within the 6-foot (1829 mm) dedicated space.



36" deep, 30" wide, 6'6" tall.

Which way does the door to the room swing?
 
#10 ·
Door swings outwards. This is a permitted job. Your lucky to have an inspector pick up the phone during work hours. Unfortunately, inspectors dont pick up their phone over here. The only other place for the panel would be in the bedroom, which the owner did not like.

Thanks for the replies!
 
#12 ·
"Door swings don't play a part in clearance" Don't mean to hijack but this goes along with an idea I was playing with for adding a subpanel for my own home shop, which also is garage. Just playing around with some ideas as I remodel my own house.

For one possible location shown in red, with 30x36" clearance shown as a crossed box, I would want to use the door opening into the house for part of my clearance.

The other possible location would be covered by the inward opening side door to outside. Wall space is in very short supply and the side door is the only wall space that won't get something put in front of it.

I only do commercial so my electrical guys just mentioned that might be a consideration but also stated they really don't know.
 

Attachments