I have to wire a 4 wire honeywell zone valve for a radiant heat zone addition to a boiler. there are two existing zone valves that are fielf wired to the boiler but the addition will be wired into a BG zonetrol ztv-4 zone valve controler. there will be a zone valve, circ pump as well as the boiler as the radiant zone has its own t-stat.
thanks
jt
 

·
Thom
Joined
·
4,137 Posts
should be two pair, reds and yellows.

The yellows are wired in series with the transformer and thermostat. The t-stat opens the valve.

The reds are a separate switch that is activated when the valve is open/closed. These attach to a relay that controls the pump.

There are a couple different ways to wire the system. They should be covered in the instruction sheet that comes with the valve.
 