My first choice is an exterior combination service entrance/panel. You don't show where the service is.

Second choice would be behind the laundry closet door. It's a personal thing but I don't like panels in bedrooms.
 

·
solar guy
Joined
·
1,917 Posts
Why would SCR be required?
I meant SER which is 4 conductors for isolating the ground and neutral as opposed to type SE which would only be three. The panel will be more than 5' from the entrance point into the building at the location shown behind the bedroom door.
 

·
I own stock in FotoMat!
Joined
·
14,144 Posts
I meant SER which is 4 conductors for isolating the ground and neutral as opposed to type SE which would only be three. The panel will be more than 5' from the entrance point into the building at the location shown behind the bedroom door.
Could you not use EMT, or rigid, or PVC, or IMC, or MC, or AC............?:shifty:

Besides, the 5' you refer to is a POCO rule, not an NEC one.
 

·
Electrical Contractor
Joined
·
2,411 Posts
This is an active thread on the JLC board as well.

IMO there would be no way to get the proper 36" clearance anywhere in the laundry room.
Also, many inspectors do not allow panels behind door because the proper clearances cannot be maintained.

An outside disconnect would be required if the panel were more than 5-6 feet inside the structure. This is in NYS.
 

·
Electrical Contractor
Joined
·
2,411 Posts
Think about it. Clearances must be maintained. This is why something a simple as a pile of boxes or other storage in front of a panel is a violation.

How can you maintain the clearance if the door can be opened? A lock?
Sure, some inspectors do allow it, but some don't either.
 

·
solar guy
Joined
·
1,917 Posts
Could you not use EMT, or rigid, or PVC, or IMC, or MC, or AC............?:shifty:

Besides, the 5' you refer to is a POCO rule, not an NEC one.
Yes you could but again inflating the cost of the service SER would be the least costly easiest solution provided it met local requirements. It would not around Chicago
I do not have a code book in front of me but I strongly believe that the 5 foot rule is a NEC requirement and not just a POCO rule.
 

·
Electrical Contractor
Joined
·
2,411 Posts
I do not have a code book in front of me but I strongly believe that the 5 foot rule is a NEC requirement and not just a POCO rule.
It is not in the NEC. A specific distance is NOT mentioned.

230.70(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
 

·
solar guy
Joined
·
1,917 Posts
It is not in the NEC. A specific distance is NOT mentioned.

230.70(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
My point was Behind the bedroom door or behind the laundry room door would require a service disconnect either outside by the meter or just inside at the point of entrance. And in that case the panel would be treated the same as a sub panel. Correct?
 

·
Capra Aegagrus
Remodeler
Joined
·
26,638 Posts
230.70(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
Aye, there's the rub. You can generally expect the point of entrance to be an outside wall, no?
 