Contractor Talk - Professional Construction and Remodeling Forum banner
1 - 6 of 6 Posts

·
Registered
Joined
·
1 Posts
Discussion Starter · #1 ·
When preforming a load calculation on a Duplex, do i need to consider it as one, or would I consider each "Dwelling" seperately? Would I do two seperate calculations or just one? Im thinking just one since there is only one feeder coming into the Two-Family dwelling, and then it is split at the 2 gang meter base. Thanks for help and very nice forum. Doesnt look as busy as I thought, but nice.
 

·
Registered
Joined
·
10,486 Posts
Without knowing the size or age of the place, I'll guess 200A to the meters then 100A to each unit, it's a popular setup.
 
1 - 6 of 6 Posts
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top