Discussion Starter · #1 ·
I'm curious about the smart technology some thermostats have which can turn on the system to allow it to reach the set temp by the programmed time. So, if at 4:00 it should be 72 degrees, it may turn on at 3:35.

I'm advising on a gymasium w/ two split system units-loose building w/ 35' tall gable ceiling. On particularly cold days the system could be turned on Saturday at 6pm and still not reach 65 degrees by 9am Sunday (normal setback is 55).

question: how effective are the 'smart' thermostat's at doing their job of getting the temp to where it should be at the designated time? Do any of them have an externally mounted temp probe (would seem smarter with this)? finally, HOW does this feature work especially with large temperature flucuations brought about by global warming :eek:

The Honeywell t-stat calls there feature "Smart Response Technology"
 

·
Pompass Ass
Joined
·
2,090 Posts
Some of the thermostats have a learning mode, where they can learn how a system operates and how long it will take to achieve a certain temperature.
 

·
Registered
Joined
·
2,515 Posts
First. if the building doesn't recover by Sunday morning when you set the stat up Saturday night.
Then a set back thermostat isn't what you want or need.
A new heating system, or an improved building envelope is what you need.

If the building is that bad at extreme cold temps. It will only let teh building drop to setback temp for a short period of time before ti goes into recovery. Which means it may run the system all night any way.


They work by monitoring how long they had to run to maintain the setback temp.

If it had to run X minutes to maintain temp, then it will have to run X minutes times 1.018 to increase temp 1°F. And new run time X times 1.017 to increase the second degree. And it calculates that how every many degrees it has to increase temp(slightly over simplified, but a good enough explanation).

Does this building have a fresh air intake. If son, it should not be opened during recovery time.
 

·
Contractor
Joined
·
4,767 Posts
Discussion Starter · #4 ·
I think the entire gymnasium structure is a fresh air intake...but not one designed into the HVAC initial installation.

Beenthere, based on your description, is it 'smart' enough to learn if the time does not reach the set temperature based on the built in table, does it increase the multiplier to increase the turn on time?

thanks for the insite.

system size: all the hot air is at the top of the room (all supplies are on the ceiling). I was on a lift once in that room and the floor area was 65 and 30' in the air it was real hot. not sure a ceiling fan would widthstand the abuse of a kickball, any other ideas for getting hot air down?
 

·
Registered
Joined
·
2,515 Posts
They have an installer setting for more aggressive recovery if you find its not reaching temp in time.

Switch to a different register. One that throws the air straight down. And use a continuous fan setting during occupied times.
 