I'm a bit stumped on this one. I'm not an electrician and working on a punchout for a job I've inherited. The comment made on this particular item is that the seal tight is not necessary for a proper installation and is not even connected properly. I think it's been connected properly and have no issue in regards to compliance with code. Thoughts?
 

Attachments

·
Goin' Down in Flames....
Highwayman
Joined
·
4,913 Posts
Well, there's a liquid-tight fitting, with liquid-tight flex, terminating into box rated for dry locations. :blink:

That might be what they are referring to.
 

·
Registered
Joined
·
129 Posts
And if you zoom in, the flex is attached to a piece of emt. I’m thinking they needed a section of flexible conduit and all they had was liquitight.
 

·
Registered
Joined
·
11,926 Posts
Is it LT with the metal core or PVC through?

If it is the second, you need a ground wire.

Tom
 

·
I own stock in FotoMat!
Joined
·
12,417 Posts
Is it LT with the metal core or PVC through?

If it is the second, you need a ground wire.

Tom
That would be what I'd check first.... whether the flex is approved for grounding and whether there's a ground wire if it isn't.


It looks like there's a gasket on the 90, so I'd say it's not an approved ground path.
 