NM is not permitted in wet locations, and anything outside the structure is considered a wet location regardless of the raceway used. 300.9 of the 2008 NEC clearly states this:
300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.8(C).