1 - 8 of 8 Posts
NICKTECH
yeah, we'd do it on a refrig. coil, or an A coil sitting aroung the shop, or on a leak that was too much of a bear to find on the job. cap an end off and braze a schrader fitting on the other end. the coil usually gives the lowside test psi. otherwise i use 150
NICKTECH
those are real bitches! ive yanked out a coil, and capped off the liquid and suction, then pressurize it with nitro. took the coil back to the shop to pressure test. if i get back to the job and the pressure is where i left it then the rest of the system is good. just easier and less aggrivating sometimes
Discussion Starter · #6 · (Edited)
LS-4 Reference Leak
Some electronic leak detectors come with a leak reference. Unfortunately these only come in one flavor test refrigerant.
In one of the IOR articles they made reference to an LS-4 leak reference. You attach it to the refrigerant cylinder open the cylinder valve then test your electronic sniffer. Has a 5 gram per year reference which is slightly more than 0.1 ounce per year.
The advantage is that you can attach it to the type refrigerant that is in the system and test your detector to make sure it works.
Have been hearing stories that some have had detectors that would detect R-22 but not R-404A.
Unfortunately at this time the only source for the LS-4 is wholesalers and manufacturers in the United Kingdom.
NICKTECH
the epa allows for use of a trace charge. a deminimus amount or r22 pressurized with nitrogen. the nitrogen pressure pushes the refrig out of a leak and the leak detect picks it up. the combo can be used in any type refrig system. 410a 404, 407 etc but you're only allowed to use r22 as the trace charge. the epa allows the venting of the mix as well.
LS-4 Reference Leak
Hello all,
I represent the manufacturer of the LS-4 reference leak, HT Products based in Sussex, UK. You are correct that we don't have a distribution network in the US but this is something we are investigating, it's helpful to hear people making reference to our products.
The introduction of our reference leaks come in response to EU regulations on HFC leakage which specifiy a minimum acceptable leak of 5g/Yr from a charged system. Engineers can check their detectors against the reference leak which has a known + calibrated value and compare the readout to the value registered on a real leak in a system, even on a cheaper leak detector with no numerical display the engineer can get an idea of how a leak under investigation compares to the minimum acceptable leak under current regulations.
As to the questions over the sensitivity of different leak detectors to different gases then the use of reference leaks can provide information on this relationship e.g. sniff one reference leak for 5g/Yr R134a and one for 5g/Yr R404a and see how the display on the leak detector compares.
some more information on our other products is available from our website, type htproducts into a search engine.
many thanks for reading
Dave Percival
HT Products
1 - 8 of 8 Posts