I know outside receptacles need to be GFCI, but am unclear on light fixtures. Any help appreciated.
 

·
Electrical Contractor
Joined
·
744 Posts
Mounted to the house are to the ground? If close to the ground or away from the house I would put them on gfci.
 

·
DGR,IABD
Joined
·
9,683 Posts
There is no NEC requirement to GFCI protect any exterior lighting. About the only time you GFCI protect lighting fixtures is for certain types of lighting installed over a certain zone over a tub or shower. Same goes for exhaust fans installed in this area. While it might be a good idea to GFCI protect exterior lighting mounted low to the ground (such as step lights and line voltage landscape lighting), there is no general requirement to do so in the code.
 