Anyone ever set an outlet into the surface of a kitchen countertop? I guess it would have to have some kind of cover in order to be code compliant in addition to being GFI protected, thanks GMOD.
 

·
Registered
Joined
·
428 Posts
Flush

Sorry

(5) Receptacle Outlet Location. Receptacle outlets shall be located above the countertop, but not more than 18 inches from the countertop surface. Receptacles shall not be installed in a face-up position in the work surfaces or countertops and they must not be located on the sides of cabinets.

I would never put them in anyhow even if someone asked me too. Things always get spilled on countertops. It would just be trouble in the long run.
 

·
Registered
Joined
·
1,300 Posts
You have to use a pop up receptacles in counter tops like on islands, etc.

I saw a really nice new one in one of my trade magazine the other day, much better looking and a lower profile than most of them I have used or seen in the past. I'll have to find where I saw it and post a link.
 

·
Electrical Contractor
Joined
·
2,411 Posts
Bubbles Thweetie: :laughing::laughing: Just a question; What about all the outlets put into the sides of Island cabinets?
What about them? They are fine as long as they are less than 12" down from the top. Lower than that will not meet the dimensions for any required counter top receptacles.
 

·
Registered
Joined
·
6 Posts
I think that he is asking why are they allowed in the sides of island cabinets and not the other kitchen cabinets?
 

·
Registered
Joined
·
428 Posts
cabinet

An inspector told me a while ago. It's what you call the area that's makes the difference. One cabinet is above the counter and one has a counter on top of it. Or maybe since it's called an island it's not really a cabinet even though it really is. Sometimes it can get confusing. I just passed a big job where I was wondering how they would enforce the afci rule. A 26 room frat house with 26 rooms with a bath and micro but not permanant kitchen facilities. It was classified an R2 which puts it in same category as motels/hotels/nursing homes/ etc... hence we didnt need afci's in the bedrooms in that instance since they were not considered dwelling units.
 

·
Registered
Joined
·
1,300 Posts
RCPainting that is the same type of outlet I saw in a different picture in a trade mag.

Gene, found out who makes the outlet, its made by Mockett. I have used Mockett's before but they were a little uglier than this one, and they also have some other new ones that are better than what they had in the past.

http://www.mockett.com
 

·
Service & Repairs
Joined
·
4,001 Posts
Very nice, Gene.


To answer the OP's question, a receptacle is not permitted to be installed flat into the counter in a dwelling, but this install is permitted in a non-dwelling setting. Go figure.
 