Looking for Ideas for an excavation

5027 Views 26 Replies 13 Participants Last post by  Upchuck
I am getting ready to bury a 10,500 gal water tank for a fire suppression system. The tank is going in the ground 9' from an existing building, the top of the footing is 5'8" below grade(1 foot footing). The dimension of the tank is 13'2" top to bottom, with either 12" of stone under it or on undisturbed soil, there is a 4' round sump station located 5-10' away from it/building that is 4'8" deeper than the bottom of the tank.
My question is this: the tank was supposed to go in back in the early part of sept when the water table was much lower, but the engineers and precast co have been redesigning if for the last month and a half and the water table is up substantially, finish grade on top of the tank is 410' and the water table is at 394.
I need to make sure that the building does not shift but with the water up I am worried about the 45* slope leading up to the existing footing is going to undermine. Driving sheet piling will cost 22K, I was going to underpin the corner originally, but with the water up that doesn't seem like a good idea. I obviously will de water and drop the table some, but am nervous about the proximity of the building. It is up to me for BMP to design the support.
Any ideas?
to add insult to injury the engineers wont answer the questin how much ground cover over the tank.:laughing: I guess it is not that important

Thanks in advance.
John
1 - 1 of 27 Posts
If the cobbly river gravel that you have to dig in is anything like it is over here, you will end up with a hole at is much larger than you need. That type of ground just doesnt hold up well during excavation, the banks cave constantly.