1 - 19 of 19 Posts

· Registered
Joined
·
255 Posts
Discussion Starter · #1 ·
I put this 200 amp service in yesterday and ran a #4 (Bare Armored Ground) GEC to a water pipe, but since the wire was too big for the grounding bus in the panel, I split it between screws. I can't find any violation in the book, so I wonder if this is code compliant? Looks like my pic is sideways, but this is a Murray all-in-one panel.
 

Attachments

· Registered
Joined
·
876 Posts
I agree it is a code violation and not necessary. I twist the wire tight with my pliers and it slides in pretty easy.

But what is the reasoning behind the code in this case? Practically speaking it will work and you could even argue that it is less likely to fail completely because of the double connection.

Good Luck
Dave
Right on Here !
One other Thing, You don't need ground rods in LA ?? Here, you need 2 Ground rods 6 ft apart with a continuos loop from the Panel & the Inspector may even have you also run to the water main coming into the Structure....................
 

· Registered
Joined
·
255 Posts
Discussion Starter · #5 ·
Ya know, I didn't even try to get it under one screw, OK, live and learn. Yes, here in Los Angeles we run a #6 to a single ground rod. I've never installed nor have I ever seen a second ground rod.

Thanks guys
 

· Registered
Joined
·
428 Posts
Mr. Mike

Have this printed out for your inspector next time he ask's you for 2 ground rods.

2008 NEC—250.56

Resistance of Rod, Pipe, and Plate Electrodes.

A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(4) through (A)(8). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft.) apart.

The requirement for a single electrode that does not have a resistance of 25 ohms or less to be augmented does not apply to any electrodes other than rod, pipe or plate. It is required to augment such an electrode with one additional electrode of any of the types specified by 250.52(A)(4) through 250.52(A)(8) so 250.52(A)(1) for underground metal water pipes, 250.52(A)(2) for metal frame of a building or structure, and 250.52(A)(3) for concrete-encased electrodes were deleted from the list of permissible electrodes to be used for augmenting the rod, pipe or plate electrodes.

Just like a criminal case. It's up to them to prove it's not 25 ohms or less. Not your problem. Although, you'll be getting turned down for screws on covers missing and things like that for the next 2 yrs.
 

· Registered
Joined
·
384 Posts

· Baltimore Electrician
Joined
·
1,253 Posts
What is the violation?
That neutral/ground bar has certain wire sizes it has been tested for/is rated for. 1/2 of a #4 isn't one of those sizes.
Besides, as Speedy said, that #4 will fit into one of those terminals.
 

· Head Grunt
Joined
·
3,540 Posts
Have this printed out for your inspector next time he ask's you for 2 ground rods.

2008 NEC—250.56

Resistance of Rod, Pipe, and Plate Electrodes.

A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(4) through (A)(8). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft.) apart.

The requirement for a single electrode that does not have a resistance of 25 ohms or less to be augmented does not apply to any electrodes other than rod, pipe or plate. It is required to augment such an electrode with one additional electrode of any of the types specified by 250.52(A)(4) through 250.52(A)(8) so 250.52(A)(1) for underground metal water pipes, 250.52(A)(2) for metal frame of a building or structure, and 250.52(A)(3) for concrete-encased electrodes were deleted from the list of permissible electrodes to be used for augmenting the rod, pipe or plate electrodes.

Just like a criminal case. It's up to them to prove it's not 25 ohms or less. Not your problem. Although, you'll be getting turned down for screws on covers missing and things like that for the next 2 yrs.

Thanks for the info, if memory serves me when i spoke to the inspector about this several yrs ago the 2 ground rods and 6' apart application was a requirement by the POCO. I have gotten away with using an existing ground pipe and one ground rod in the past as long they were 6' apart and continuous loop. I have found it is easier to just ask the inspector what he wants to see when i am in doubt. Makes life much easier.
 

· #1 stunner
Joined
·
580 Posts
That neutral/ground bar has certain wire sizes it has been tested for/is rated for. 1/2 of a #4 isn't one of those sizes.
Besides, as Speedy said, that #4 will fit into one of those terminals.
Exactly. Thank you John. :thumbsup:

So what is the violation? is art 110.3 (b) ?
 

· Service & Repairs
Joined
·
4,536 Posts
That neutral/ground bar has certain wire sizes it has been tested for/is rated for. 1/2 of a #4 isn't one of those sizes.
Besides, as Speedy said, that #4 will fit into one of those terminals.
They fit alright but just barely.

OP: I would suggest getting a lug and attaching it to the ground buss if you're having issues getting that #4.
 

· Registered
Joined
·
876 Posts
Thanks for the info, if memory serves me when i spoke to the inspector about this several yrs ago the 2 ground rods and 6' apart application was a requirement by the POCO. I have gotten away with using an existing ground pipe and one ground rod in the past as long they were 6' apart and continuous loop. I have found it is easier to just ask the inspector what he wants to see when i am in doubt. Makes life much easier.
I think your right on here Paul- it is in the National Grid Service Guidelines book on the 2 ground rods- which it seems to have been this way for many, many years. It has been just automatic for me to use 2 rods.........
 

· Baltimore Electrician
Joined
·
1,253 Posts
They fit alright but just barely.

OP: I would suggest getting a lug and attaching it to the ground buss if you're having issues getting that #4.
I agree, #4 stranded can be tricky - #4 solid is no problem. I like to have a few lugs on the truck for these situations.

I'll be honest - I did it the way shown in the OP for a long time, before it was pointed out to me that it was a violation.
 