Discussion Starter · #1 ·
I installed a General Aire 1042 for a customer in a 2000 sq' house. On a high velocity system. The system is wired properly cause the solenoid opens and water flows on a call for humidity. The customer has a hygrometer upstairs and registers 27% relative humidity. We can't get the RH up any higher is the problem. New house. New air handler. High Velocity system works well enough according to the customer. Humidifier is attached to the return with a 2"insulated bypass from the 8" supply on top of the air handler. Water supply was recently changed to the hot side hoping that would help with no success. The side of the humidifier is a 6" opening that I've installed a 6"cap and attached the 2" bypass as per the air handlers manufacturers instructions. Yes, the damper is open. Has anyone got any suggestions?
 

·
Registered
Joined
·
2 Posts
Discussion Starter · #4 ·
What humidifier would you recommend? Yes, 2" bypass. It's for a high velocity air handler. 2" is recommended by the air handlers manufacturer.
 

·
Registered
Joined
·
2,510 Posts
When you connected it to the hot water line. Was this the how water pipe at the water heater. Or just one that was near the humidifier? Needs to be at the water heater. Can't be bigger then 1/4" either, and you may need to insulate it. Have the water temp set up to 140°F.

What is the air handlers heat source. Is it a hydrocoil, electric strip? Is the bypass before or after the heat source.

Probably should have ran a 6" pipe off the humidifier for about 2 foot, then attached the 2" line. So more of the humidifiers pad got air going across it.
 