GFCI On a sump pump

17K views 49 replies 9 participants last post by  GettingBy  
#1 ·
Can anyone tell me why a sump pump is on a GFCI circuit?

This particular sump runs every 7min in the summer when it's wet. It worked for 4.5 yrs and now it is tripping.

These GFCI's are so crappy now a days, I wouldn't put them on any circuit that I really needed power.

Am I crazy or do you agree there should be a dedicatr 20amp circuit for a sump that if the power goed out for 4 hrs the basement will flood?
 
#2 · (Edited)
Some GFCIs with higher patent numbers may be able to handle motor loads without nuisance tripping. IMO, the motor winding capacitance to the housing is the problem, in addition to the inrush current.

I'm not a sparky and I don't know the NEC but I'd just run two independent ground wires so that an internal motor failure cannot possibly shock anyone.

For $16 you can get a water level alarm.

Knowing the 7 min on(?) and how many min off(?) and what size pump(?) you can size a battery/inverter system for this. You also need to know how long the power may be out.

A 5A, 120v motor at 50% duty cycle for 24 hours needs 7200 watthour storage.

If you measure the sump refill rate (easy) you may find you can use a smaller pump. The duty cycle will also tell you this.
 
#6 · (Edited)
"US Patent No. 8,500,412"

That is a high patent number. :)

So 50 PSI with a 10' head gives you 13 GPM plus a water-powered alarm. Way good, assuming your water supply doesn't fail when your power fails. And with 70% efficiency [sort of] it's as good as an electric pump.

I'm surprised http://www.nema.org/pages/default.aspx doesn't sue the inventor for 'restraint of free trade' or some such thing.
 
#8 · (Edited)
On many jobs we use a single dedicated outlet for sump pump. We have also used the water powered sump pumps, while costly they work very well. For every gallon of water used it pumps out 2, noisy though. But it keeps the water out, much better than battery powered pumps

the one tom posted is the same one we use, needs 3/4 water line at sump, backflow preventer, above ground discharge etc
 
#22 ·
Normally I would agree with you with the NEC code stepping to far but as you just mentioned if the GFCI is tripping then there is a fault with the unit. Simply checking resistance from the ground terminal to the common of the pump plug would verify this. Now even if it trips the GFCI but works normal on a non protected circuit is it still safe to use? Do they put it on a non protected circuit and wait for the fault to become bad enough to trip the breaker or have someone get injured?

IMO anything directly dealing with water where a person may have in contact should be GFCI protected. Where I think the NEC stepped a little far is the requirement of a GFCI circuit for say a fridge or freezer in a basement/garage area. I myself put those on dedicated circuits so I don't chance a loss of thousands of dollars in food over a faulty device.
 
#21 · (Edited)
Since the NEC may not budge, does anyone make motors that are specifically designed to work reliably with GFCIs?

For starters, they'd have a very low winding-to-case capacitance and maybe a low inrush current (achieved electronically).

Of course, doing so would admit that there is a problem. :(

BTW, with vehicle problems that the dealership has not admitted to, there is always 'the aftermarket'. There doesn't seem to be a parallel in this situation.
 
#24 ·
Can someone show me where a sump pump is required to have a dedicated or individual branch circuit? I under stand if the pump draws more than 10 amps on a 20 amp circuit that there is an issue based on 210.23(A)(2) if the pump is fastened in place. I have not seen any that were fastened.

The point is I have never seen an article that requires a sump pump to have a dedicated circuit. I search the NEC pdf and still have not come across that requirement
 
#27 ·
From 2002
http://ecmweb.com/code-basics/nec-requirements-ground-fault-circuit-interrupters-gfci

However, the Code does note a few exceptions to these rules: GFCI protection is not required for receptacles that are not readily accessible or are located on a dedicated branch circuit and identified for a specific cord-and-plug-connected appliance, such as a sump pump. (means no duplex outlet)?

It may have changed since then.

BTW, I am about the last person in the world to help an electrician, if I have this time.
I don't know the NEC and they mostly no likey me!:no:
 
#30 ·
If I remember correctly a dedicated outlet ( single ) not a dedicated circuit, is what my electrician said.

A faulty gfi on a sump pump can ruin much more than a freezer full of food, I have a customer who knows this first hand. Almost 2 ft of water in the basement, now they have single non gfi outlet and 2 water alarms.