huntington beach, ca.
Joined
·
362 Posts
Discussion Starter · #1 ·
I need a 2 hour override for lighting in medical building, lights operate off a 20 amp contactor. I have no idea where to start looking...something push button would be nice.
 

·
Registered
Joined
·
838 Posts
I'm thinking you have many lights to operate, as you said they were on a 20 amp contactor so you will need a timer with heavy duty contacts............. If you want a push button type switch?, you will have to wire it to pull in a timer relay to operate that 20 amp contactor. Need more Specifics !
 

·
I own stock in FotoMat!
Joined
·
12,611 Posts
I'm thinking you have many lights to operate, as you said they were on a 20 amp contactor so you will need a timer with heavy duty contacts............. If you want a push button type switch?, you will have to wire it to pull in a timer relay to operate that 20 amp contactor. Need more Specifics !
I'm gonna say it's the lighting circuits that are 20 amps, not the coil on the contactor. I've never seen a lighting contactor coil draw more than an amp.
 

·
Registered
Joined
·
4,732 Posts
Similar situation..folks place.

Have a gas well that needs saltwater pumped periodically..as needed. We have a pressure switch on a volume tank that will start it..but it needs to run for like an hour after the pressure comes back up.

Timer won't work... need some thing like a relay w/delay?
 

·
Registered
Joined
·
7 Posts
Sparky is right. If you install just a push button, you'll need to install some type of timing device that hooks up to a 7-day timer. It is best to install a twist timer that mechanically times itself out that is wired to a lighting contactor.
 

·
huntington beach, ca.
Joined
·
362 Posts
Discussion Starter · #7 · (Edited)
I'm thinking you have many lights to operate, as you said they were on a 20 amp contactor so you will need a timer with heavy duty contacts............. If you want a push button type switch?, you will have to wire it to pull in a timer relay to operate that 20 amp contactor. Need more Specifics !
I'm using the 365 day time clock on the right in the picture, so basically you are saying this levinton 6652 push button, will most likely need a relay to close the lighting contactor. If this is the case, not a problem.
 

·
Professional Remodeler
Joined
·
2,289 Posts
I need a 2 hour override for lighting in medical building, lights operate off a 20 amp contactor. I have no idea where to start looking...something push button would be nice.
We used to use something like this in the stores we did. just a simple off-delay relay that controls the coil of the contactor.

http://www.grainger.com/Grainger/items/1EJP3

Turn the light switch off and the contactor turns the lights off after predetermined amount of time (ie. Give the employees enough time to get out of the building before all the lights went off)
 

·
I own stock in FotoMat!
Joined
·
12,611 Posts
I'm using the 365 day time clock on the right in the picture, so basically you are saying this levinton 6652 push button, will most likely need a relay to close the lighting contactor. If this is the case, not a problem.
You can put the 7-day timer and the 2-hour switch in parallel with each other. That way, either one will turn on the lights as needed. Run them with the same circuit to control the same relay.
 

·
huntington beach, ca.
Joined
·
362 Posts
Discussion Starter · #10 ·
You can put the 7-day timer and the 2-hour switch in parallel with each other. That way, either one will turn on the lights as needed. Run them with the same circuit to control the same relay.
Yeah I understand, I know some of these timers won't close contactors. But this one says its good for inductive loads/motor loads.
 

·
Registered
Joined
·
838 Posts
I'm gonna say it's the lighting circuits that are 20 amps, not the coil on the contactor. I've never seen a lighting contactor coil draw more than an amp.
???? Lighting circuits are never across the coil of the Contactor. The lighting is across the contacts of the Contactor. The coil is usually pulled in by a relay or remote switch, etc- most times thru a Photocell. We had multiple outside area lights turned on by one contactor with just one photocell to turn them on.................
 

·
I own stock in FotoMat!
Joined
·
12,611 Posts
???? Lighting circuits are never across the coil of the Contactor. The lighting is across the contacts of the Contactor. The coil is usually pulled in by a relay or remote switch, etc- most times thru a Photocell. We had multiple outside area lights turned on by one contactor with just one photocell to turn them on.................
I think we said the same thing.

It's the lighting circuits that use 20 amps, not the coil. Sometimes it's the same circuit, but the coil won't use 20 amps when pulled in.
 

·
ampman
Joined
·
783 Posts
We used to use something like this in the stores we did. just a simple off-delay relay that controls the coil of the contactor.

http://www.grainger.com/Grainger/items/1EJP3

Turn the light switch off and the contactor turns the lights off after predetermined amount of time (ie. Give the employees enough time to get out of the building before all the lights went off)
this is what is needed timers will need to be reset in the event of a power outage unless they are battery backed up ,make it to complicated and "employees" will not get it
 