Greetings. Here's the deal. Bidding on a job to run a 60 amp feeder from a house to gate controller area and set a 60 amp Sub-Panel. Future draw shouldn't exceed 30 amps max. Voltage drop was about 4%. It's a 650 ft run.
Personally, I would rather run #2 Al quadplex and bury 2.5ft deep. My total cost of trench and wire $2,100.00. If I do 1.25" Pvc Sched 40 and 3-#4 Cu's and 1-#6Cu (Competitors bid) it would be 4,570.00 plus several more hours labor. Question is how many of you bid on Cu and why for something that long. How many Al and why. People around my area are still freaked out when you say your running Aluminum. It's hard to explain to them it's used everywhere. I could even throw in a 2 pole 60amp GFCI breaker if they want some extra safety. Does anyone other than puco make runs that long in Cu anymore??
 

·
Registered
Joined
·
428 Posts
Discussion Starter · #7 ·
really

explain in further detail. You talking landscapers digging to deep cutting into them or ones buried to shallow or just rocks and stuff damaging them in settling? Or something else. Do tell
 

·
Registered
Joined
·
428 Posts
Discussion Starter · #11 ·
underground

out where I am it's usually very nice dirt/clay with no rocks at all. We usually put it in 2.5 ft deep to be safe. Never had a callback yet. We have repaired a few as well. One was where they dug a basketball base and just cut one phase. Others were mostly from landscapers and one was the wire was nicked from a big rock butted up against it slowing cutting it over the years. I could definately see in other areas with rock that would be the best plan.
 