Performed a walkthrough with a potential client and came across this framing of floor joists/wall connection. Previous contractor says it’s to code, however, I believe it violates R502.6 Bearing as there are no brackets to connect to the rim joist to transfer load to wall and the horizontal 2x4 is not a proper load transfer point as the joist is not nailed to the vertical 2x4 stud(possible attempt to perform a ribbon strip?). Looking to assist with further explanation on the violation.
Are there any other violations that can be elaborated on? Thank you for your help!
R502.6 Bearing
The ends of each joist, beam or girder shall have not less than 1½ inches (38 mm) of bearing on wood or metal, have not less than 3 inches of bearing (76 mm) on masonry or concrete or be supported by approved joist hangers. Alternatively, the ends of joists shall be supported on a 1-inch by 4-inch (25 mm by 102 mm) ribbon strip and shall be nailed to the adjacent stud. The bearing on masonry or concrete shall be direct, or a sill plate of 2-inch minimum (51 mm) nominal thickness shall be provided under the joist, beam or girder.
Are there any other violations that can be elaborated on? Thank you for your help!
R502.6 Bearing
The ends of each joist, beam or girder shall have not less than 1½ inches (38 mm) of bearing on wood or metal, have not less than 3 inches of bearing (76 mm) on masonry or concrete or be supported by approved joist hangers. Alternatively, the ends of joists shall be supported on a 1-inch by 4-inch (25 mm by 102 mm) ribbon strip and shall be nailed to the adjacent stud. The bearing on masonry or concrete shall be direct, or a sill plate of 2-inch minimum (51 mm) nominal thickness shall be provided under the joist, beam or girder.