what is the code for wiring the AC compressor disconnect? height of the disconnect box and is the lead to the compressor from disconnect supposed to be armored?
 

·
Contractor
Joined
·
4,782 Posts
Discussion Starter · #5 ·
Disconnect clearance min 30" wide 36" deep. NOT directly behind unit.
does this mean wherever the disconnect is mounted there must be open space 18" up and down (of center) and 15" left and right? what about a minimum height from ground-would that be 18"?
 