IMO the receptacle needs to be 4-conductor AND the circuit wiring needs to be 4-conductor.
If you mean do I have a 4 wire conductor at the rec, no. I am hoping I can avoid having to run a 4 wire and that the green case ground can be used in place of the grounding strap. This a Samsung unit. I have replaced many 3 wires for 4 wires on dryers a few years ago. In those cases, I just bend the ground strap back, run white to the middle terminal, black on one hot side, red on the other. The reverse had me a little confused. As of now I have the green ground wire in the middle along with the white nuetral/ground.Do you have a wiring system that will support the 4 wire receptacle?
The NEC begs to differ:IMO the receptacle needs to be 4-conductor AND the circuit wiring needs to be 4-conductor.
2008 NEC said:250.140 Frames of Ranges and Clothes Dryers.
Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be connected to the equipment grounding conductor in the manner specified by 250.134 or 250.138.
Exception: For existing branch-circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of
the circuit for these appliances shall be permitted to be connected to the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service entrance cable and the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment
Put the 3-wire cord on, bond the neutral and ground in the appliance, rest. :thumbsup:So basically it is a new dryer on existing 3 wire conductor. When I bought it, I thought I would have to run a 4 wire but was told I could just swap pigtails. When I vcame to the grounding, I had to stop and think. Thought maybe someone on here could rest my mind a little.
The cord can be changed to a 3 wire, yes the green (ground) and white (neutral) go to the same location, there will be a wiring schematic that shows you how wire the dryer, it is usually a bonding strap.Bought a new dryer and of course it has a 4 wire pigtail. Is it necessary to change the old 3 wire rec in my house, or can I just change the 4 wire oigtail to a 3 wire off the old dryer. Now if this was the opposite situation, I would have no problem. Bend the ground strap back, neutrtal to the middle, ground to the cab , good to go. Where I am a little bumfuzzled is do I put the green ground on with the white neutral at the power block?
Yes, this is a 3 wire circuit. I ran it myself a few years ago. I did not wait for an answer, just wired it the way you said to do it. I worked on appliances several years ago, but still had to stop anf think on this one not knowing if the internal wireing what I was used to.What really needs to be determined is:
Is the existing REALLY a 3-wire circuit or not?
Many times, the AC jacket is over looked as the EGC here.
I knew all new stuff was supposed to be 4 wire and thought I would have to run another circuit. But then I thought maybe existing circuit was excempt. Seems I was right.boman...if you get a chance and the motivation....make it a 4-wire.....technically, the 3-wire went out in like 1996 - but the NEC realizes many homes were built prior to that date.
EMT is a far better ground than any conductor you can fit inside of it.In the Chicago suburbs where everything must be run in emt, I sometimes wonder myself if the metal emt is a substantial ECG. We have to make our own 4th wire to the Eg via a green screw.
It's all so confusing, I just want to be a fireman or superhero when I grow up!
Is it is a newer/nicer dryer? Older dryers have 240v motors and elements. Newer dryers have 120V components on them?
Because it plugged in with the cord up, and it was bent back over just before the dryer was slammed up against it, literally folding it. You can still see the curvature of the cord caused by the torture inflicted on it............ but what happened to the plug end? ............