Im working on a old Wise furnace, circa 1962. Natural gas 82K BTU. Its an old power pile system. The gas valve is a honeywell vs820a1047. It is in my mothers house.
The symptom is the pilot stays lit but the gas valve wont open and light the burner.
I disconnected the thermopile wires from the gas valve and lit the pilot. After about a minute it was producing just over 600mV with no load.
I reconnected the TP to the gas valve and checked voltage. I saw around 140mV.
The t-stat and limit switch are wired in series. I removed those wires from the gas valve and put a jumper from the TP terminal to the T-stat terminal on the gas valve. It worked just fine. Gas valve opens, burner lights.
I reconnect the limit switch and t-stat to gas valve. The valve will not open. I checked voltage and there is only around 80mV under load. Not enough to operate the valve.
I checked resistance thru the limit switch and t-stat. It was just over 2 ohms.
So the questions are:
1. Is the thermopile just too weak to provide the needed voltage? It looks original
2. Is the thermopile OK and the resistance of the limit switch and T-stat too high at 2 ohms
3. If it needs a thermopile, does anyone know where i can find one like in the photos?
One of our direct employees is an old HVAC/furnace man. He is stumped.
Our local supplier wasnt much help. They kind of looked at me funny when i started talking about a mV gas valve. One guy knew what i was talking about and said he might be able to cross something if i bring the parts in.
Ive got an account at Lennox but those folks dont seem very helpful. All they know are part numbers.
Mike-B is online now
Old 10-28-2018, 09:17 PM   #2
hdavis's Avatar
Rewards Points: 3,862
Re: Thermopile/millivolt Generator
Those resistances should be well below 1 ohm.
Power from the TP is V^2/R. Get R too big, and there isn't enough power.
I'd start by cleaning the connections.
You also need to clarify where the 80 and 140 mv readings were taken
hdavis is online now
Fouthgeneration (10-31-2018)
Old 10-28-2018, 11:24 PM   #3
Mike-B's Avatar
Rewards Points: 902
The 140mv reading was taken at the 2 terminals on the gas valve that the ThermoPile connects to. The T-stat and limit switch were also connected to their respective terminals but t-stat was turned off.
With the t-stat on and calling for heat, the mV dropped down to 80. I was measuring this at the gas valve. One lead on the terminal that the t-stat connects to. One lead on the + terminal that the t-pile and limit switch share.
There are only 3 terminals on the gas valve. Two are for the thermopile. The + side of the TP has a 2nd wire on the terminal which sends power up to the limit switch, thru t-stat, then back down to the 3rd terminal which operates the gas valve.
Total resistance was about 2ohm in the t-stat/limit switch circuit. Up and back thru T-stat alone was about 0.2ohms so that's good. Up and back thru limit switch was about 1.9. I pulled the wires out of the limit switch. They were shiny copper. I made sure they were well connected on both ends. No difference.
Guess i should have bypassed the limit switch to see if eliminating that resistance fixes the problem. Seems to make the most sense at this point.
The existing TP/pilot setup is a honeywell cs82A. Basically extinct. If eliminating the limit doesnt fix it, i think i will order a new pilot/TP setup. I'll throw the new TP in temporarily just to see if it fixes the problem. If so, we will retrofit a new setup in place if the old "matchbook"
The Following 2 Users Say Thank You to Mike-B For This Useful Post:
Fouthgeneration (10-31-2018), hdavis (10-29-2018)
Old 10-29-2018, 08:36 AM   #4
Mike-B's Avatar
Rewards Points: 902
FYI for anyone working on this old shtuff.
Honeywell CS82A is the pilot assembly including thermopile.
Honeywell Q302A 1025 is the thermopile/powerpile/millivolt generator only.
I was able to dig up a Q302A on ebay.
Will probably buy a limit switch too and see what fixes it...hopefully.
The Following User Says Thank You to Mike-B For This Useful Post:
hdavis (10-29-2018)
Old 10-29-2018, 02:25 PM   #5
Contractor of the Month
Inner10's Avatar
Trade: Control Systems
Rewards Points: 4,152
Sand the probe, she will put out a few more volts.
Inner10 is offline
Old 10-31-2018, 07:32 PM   #6
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 8,581
Buy your Mom a New furnace or at least a 90%+ efficiency used one.
Seriously, that furnace is older than I am...
ALL parts have past their design lifetimes, especially the firebox plenum/ heat exchanger= CO and CO2 poisoning = No Momma.
Lower gas bills = More inherited money....
If you are stubborn, try a couple of added ground straps to make sure the electrons can complete the circuit.
A little low pressure canned air & a gentle vacumning wouldn't hurt.
Make sure the thermocouple well is wholely in the hot spot, maybe try turning up the Pilot gas flow for one more year's heat if you can't replace it now.
Your limit switch is out of tolerance According to web consensus...Replace and post again please.
Fouthgeneration is online now
Old 11-01-2018, 06:50 PM   #7
Mike-B's Avatar
Rewards Points: 902
We have ignition!
New limit switch and new millivolt generator installed today.
She runs like a champ.
Fouthgeneration (11-03-2018), hdavis (11-01-2018)
Old 11-12-2018, 07:34 PM   #8
daffysplumbing's Avatar
Trade: plumber
Rewards Points: 880
Funny!!! I've been doing heating for more than 50 years and never called a thermocouple a thermopile. I had to look it up.
Regardless, a good thermocouple generated 750 millivolts (3/4 of a volt) and the only place I can find a 750 mv thermocouple is at Johnstone supply. Every thermocouple we purchase at supply houses generates about 350 millivolts or only 1/3 of a volt.
Test the thermopile with an volt meter and set to millivolts. If you are not getting 320 millivolts then that is the first thing you need to change.
We also test valves by wiring a 1.5 volt battery across the thermostat wires and this will tell you whether or not the valve is functioning. If the valve does not work flip the positive to the opposite wire.
I always disconnect the thermostat wires to test the voltage. This helps to tell when wires are corroded, or are twisted together somewhere and have bad connections.
daffysplumbing is offline
Old 11-14-2018, 04:13 AM   #9
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,182
Well thats good. Cause a thermocouple is not a thermopile.
beenthere is offline
The Following User Says Thank You to beenthere For This Useful Post:
hdavis (11-14-2018)
How to properly hook a generator up to a plug to run sump pump reweb Electrical 4 01-19-2017 11:50 PM
Generator caught on fire today Burns-Built Tools & Equipment 11 10-13-2014 07:05 PM
generator sizing te12c02w Electrical 1 06-28-2012 07:56 AM
wiring a generator powered hunting shack CNC General Discussion 2 08-18-2009 10:31 PM