I've heard statements like this;
"When a condensing boiler is not in condensing mode efficiencies can be as low as 70%"
One specific condensing unit says 91% efficient and shows
Input 105 btu
Doe 97 btu
Net 84 btu
I see net ibr as around 88% with these numbers and all specs I see show similar.
How does one come up with efficiencies as low as 70% when IBR is in the upper 80's?
If efficiency was 70 ish % how could ibr be 84 kbtu?
Using 70% of the 105 kbtu input the IBR could be no more than 73.5 kbtu and therefore how could one size a boiler using these efficiency numbers?
I'm not getting this!
Kirkhj is offline
Old 05-03-2019, 09:33 PM   #2
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,252
Re: Mod Con Efficiency
Generally said by people that are not pro mod/con.
Input 105 btu
Doe 97 btu
Net 84 btu
A condensing boiler operating at a water temp of 180F, will still be at least 80% efficient. Some designs higher yet.
beenthere is offline
Old 05-04-2019, 07:53 AM   #3
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
"Generally said by those not pro modcon"
Absolutely true!
"Been There" Thanks. Maybe you could answer a few more things for me. Allow me to explain. Hopefully you'll bear with my rambling I'm so infamous for on here.
This 1980 ish weil standing pilot 150 input 104 IBR according to the label, heats the 500 ish feet of pipe and cast rads in this old house extremely well but is very tired as it was poorly maintained.
In comparison to several neighbors, local contractors and past homes I have lived in, my gas bill is suprisingly low, but obviously could be better. Main thing is I want to make sure something KEEPS heating the house.
The past 3 winters I have educated myself with a lot of help from guys on this site and other avenues. Through my past experiences with sealing up old homes, and the new tweaking and adjusting I have learned to do with all of your help (first residential boiler I have had)the results are evident. This past winter was the coldest of the 3 here I've seen yet. For more than 3 weeks steady the temps stayed well below advertised design temps, and the average temps were worse, this boiler still had no problem at all keeping up AND the total gas usage is still lower than the first and second winters.
My heat loss calc ( which I have painstakingly done) says somewhere around 88 mbu. Judging by how this boiler cycles and heats the house, and by using IBR stated on this boiler, I have great faith that this number of 88 mbu is extremely close.
Assuming that my gross output IS still 120 k and assuming that this arbitrary IBR rating of 104 k IS actually what I'm seeing, that 88 k heat loss using the IBR as my gauge for new boiler sizing should be my number?
Design temp here is -21 F
My chosen design temp for heat loss -28F
Temp for 3 weeks here ( coldest it's been in many years) -35 to - 40 F.
Rarely came up to design temp and boiler still ran cycles. Even on the very coldest highest windchill day of the full winter the boiler never ran for more than an hour and a half and would shut down at limit of 170 or if therm was satisfied first would shut down for 20- 30 minutes.
On some of those cold days I would raise the temp to 75 and the thermostat would eventually be satisfied...
I am limited to contractors here.
There won't be much available in terms of service.
Full modcon would be nice but given my situation I'm not sure that's the smartest route to go.
Weil mclein is common here and all considered...
First option IF the pro agrees;
GV 90+4 is cast iron and condensing simplified.
105 in 97 doe 84 net (Hence the inquisition on efficiencies)
The same thing I like about it is the thing I don't. Internal circulators. Common taco 007's variable speed controlled by IBC.
Large 2" waterways.
Eliminates the chimney (adding indirect DHW as well)
Eliminates the use of indoor combustion air.
Efficiency at 91%
Eliminates need for thermic boiler protection and bypass.
Second option; IF the pro agrees( likely would be their choice. Remains to be seen)
Weil Cgi 5
119 in 100 Doe 87 net
Induced draft (seems to me that consensus here is get rid of that chimney!)
Must add thermic boiler protection (ESBE) and bypass, which I would deem to be more reliable and more energy efficient vs built in circulators.
What will change either way:
Adding primary secondary.
Adding indirect
Changing from 1 zone presently circulated by 15-58 on return side to 2 zones circulated by variable speed, (on secondary supply sides I believe would be correct.)
There are 6 supply and 6 return lines on a "header" which can be split into 2 sets of 3, each set of 3 could be circulated by 1 delta t variable pump. Since 1 pump works fairly well with all 6 at now, thought is that 2 sets of 3 will allow a bit more control. One end of the house is a little slower to respond and a little cooler. ( 3 supply and returns)
Pro advice will be the final determining factor here of course.
If I had one of you guys out here modcon WOULD go in.
I'm pretty sure I've found a pro. Highly experienced boiler installer with long term business out here. Takes the time to challenge me, listen and advise but leary on modcon so...
Kirkhj is offline
Old 05-05-2019, 04:10 AM   #4
beenthere's Avatar
Trade: HVAC
Main draw back of a mod/con is the lack of either contractors that understand them, or distributors that stock parts for them. So your right to be a tad leery of one of your contractor doesn't normally install them.
DOE rating adds in all heat that enters the house from the boiler, including the heat from the boilers jacket and the piping in the basement. IBR only considers the heat from the water flowing through the boiler in its heat rating.
Primary secondary is the way to go with the boiler piping. Along with direct venting, as that will actually lower your homes heat loss a bit.
The CGI series is a long standing staple of Weil McLains, truely tried and tested.
Personally, I prefer the Weil McLain Ultra series over the GV.
Makes sure all heat zones get their 4 GPM water flow rate.
https://www.supplyhouse.com/Weil-Mcl...xoCjqEQAvD_BwE
Old 05-05-2019, 09:37 AM   #5
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
There are so many reasons to get a mod con, but yet so many in my specific situation as to why not. Still pondering. That's why I'm here!
That big ol masonry chimney, most on here seem to agree, should be closed up, newer lining or not.
From what I've learned on here and read elsewhere, I agree as well. Might make a good air intake? Is that feasible?
Please understand my concerns...
My experience with industrial modulating units is also one of the reasons I am leary. It seemed like the only units that ever posed a problem, and seemed to happen often, were(4-19 million btu.) two MUA and two heating units. All were m-trac controlled and less than 2 years old at that time (electrical work and troubleshooting is a strength I possess btw.) It was almost always related to the modulation in one way or another. All of the other units in that facility such as 2 stage conventional, radiant tubes and even mid eff residential funaces in specific areas that did NOT modulate had very few issues and were very easy for me to troubleshoot...
I am NOT a pro but was in charge of maintenence at a 65,000 Sq. ft. Welding, sandblasting, coatings shop built in 2005 because I could figure out and fix things and keep that shop running.
The m-trac modulating units I could not, for the most part, figure out. Even the pros I had to call out on several occasions had difficulties. They are complex. So...
If the pros out there were having problems with modulating gas systems, and the pros out here are afraid of the modulating residential units because they do not understand them and they are smart enough to NOT want to install them because they do not understand them, then that is very good reason to make me leary of them!
Do you agree?
Like I said if I had one of you guys out here modcon WOULD go in.
GV does not modulate. Likely not an accurate comparison, but this is where I'm at!
The gv seems pretty simple among other things, but is a weighty beast at 350 lbs. Narrow steep basement stairs, but I really like the cast iron/ss hx idea with this 115 year old black iron pipes/ column rads 80 ish gallon system...
For cast aluminum that ultra sure has chunk, but it is cast aluminum. Should that worry me because it does!
Over 200 lbs surprises me. Floor standing, awesome controls and general consensus seems to be that this is one amazing unit.
Come install one for me please. Lol
I managed to get someone from the city here who wanted to install an ECO, admitted he never has, (thats the approach I like!) and really was Gung ho about it. As he dug deeper he started seeing several issues I am and was aware of, and he changed the quote 3 times. I think he started realizing modcon here was not a simple task. I have since realized how I myself can overcome some of these issues, such as how and where to place intake and exhaust, and how and where to pump condensate. (brick house, stone foundation, windows everywhere, cast iron drainage pipes, lack of floor drains ,etc)
He also said he simply would not install a GV here and I can't remember why.
There is a company I have not approached yet 1.5 hours away. They specialize in making modular boiler boards and market the fact that heat loss etc MUST be done. They insist hydronic heating is a SYSTEM, not just a unit and that is IMO the only correct approach! All they do is boiler stuff. That I like.
They also sell only Trinity (HTI?) and pricing seems really good on the units themselves (yes they actually advertise the price to the public!) But I really don't think brand has much of anything to do with this. I truly do believe from everything I've read the last few years, that 98+% of mod con or ANY boiler fails has to do with contractor. It's rare and almost impossible to find a boiler review of a system in a heating contractors own home that is problematic and trust me, I've read hundreds. Lol
A review of my infamous rambling again
:0)
Kirkhj is offline
Old 05-05-2019, 12:59 PM   #6
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
It's also important for me to consider...
Annual service costs.
Ultra vs eco vs gv vs cgi
Repair costs.
Full mod con can be/IS expensive to repair...
The standing pilot I now own costs almost nothing yearly. Cleaned and repaired by me. A thermocouple cost me 20$. New expansion tank 30$ new tridicator 30$ Inspected by a pro under 75$. But it's old and has to go.
Seems that if I simply changed out this 150 input to a 119 input cgi and it produces the same output, I effectively would gain a 20% ish fuel saving? What is a realistic number?
This old standing pilot natural draft doesn't even have a flue damper on it!
Let's assume I change this out for that cgi and assume a 20% saving. That's 400ish$ a year and that includes our big full gas kitchen stove. Ill be eliminating that electric hwt which will lower my electric bill far more than the increase i will see on the gas bill.
For an extra 1000$ up front the gv saves what another 50$ a year?
If all this is true seems like the roi on a cgi could be my best bet?
There again comes in the simplicity and questions that I need to ask my pro.
How much is each one going to cost me yearly and how much will I really save?
You know how much an ultra service costs to service and maintain in comparison to say a cgi. I have no idea and I can't do it myself because that'll kill the warranty...
Kirkhj is offline
Old 05-05-2019, 08:44 PM   #7
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,831
If your boiler is Natural Gas fired, you can count meter revolutions per (30 seconds?) a period of time while the boiler is firing to check to see if you are over or under inputting the unit, its is part of checking regulator and jets setting/sizing during installation..
Fouthgeneration is offline
Old 05-06-2019, 04:40 AM   #8
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
Fourth Gen great idea.
Kirkhj is offline
Old 05-06-2019, 05:58 PM   #9
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
Fourth Gen I almost left work early so I could run this test. Lol
So input is rated at 150 and The test shows around 144 in. I ran a full 2 minutes with a stopwatch. The meter was replaced in November.
I believe the altitude here is 856' above sea level so all considered it sounds like this boiler is drawing about what it should?
So now does this mean my IBR, rated at 104, would be very close. The math shows an IBR of around 100 now with that corrected input.
Sound right?
Kirkhj is offline
Old 05-19-2019, 07:54 PM   #10
EricBrancard's Avatar
Trade: GC/Remodeling
Rewards Points: 986
A lot of people focus on the con side when the mod side is more impressive. If you don’t grossly oversize the thing and select one that has high turndown, then you get the benefit of the boiler using nowhere close the the BTUs of a regular on/off unit. So instead of comparing two units of equal BTU and trying to figure out the efficiency % between them, think about how the modcon will be able to step down, maintain longer burns at lower inputs therefore getting to the more efficient numbers. Where the regular boiler turns on full tilt no matter how much actual heat is needed, satisfies demand to quick and then turns off. Never burning long enough to reach its efficiency.
EricBrancard is offline
Old 05-20-2019, 10:30 AM   #11
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
Eric thanks.
I actually do fully understand the advantages of modulation and higher turndown ratios, importance of minimum firing rates and the stable temps etc that would bring, but I'm also trying to make decisions based on many different factors. Correct sizing in a big old house like this is not as straight forward as one with known values. Part of my sizing is being based on how this boiler responds on the absolute coldest of days. I'm 99% sure my heat loss calculation is correct, providing all is correct with this present system. At 10 degree below design temp it's still difficult to get a 20 delta t with this 15-58. 22 is about it. That tells me the pump could be a bit larger and that I could get more output with a better circulating system, which I would like to split into two zones.
This is also based on a high limit of 170. At least that's how I see it. If a pro disagrees then I will stand corrected. The ibr of this old boiler should be around 100 based on the input calc and I estimate 88 ibr should be plenty as a replacement with 80 being minimum.
I also do not have a lot of options out here. Minimum firing rate and ability to modulate are not as important to me as control of circulators and dhw and hopefully something that just keeps working!
I would likely have a modcon in here right now, had the first contractor answered my #1 questions on the tt solo they wanted to install and the cost wasn't so high.
Have you installed many and have you had problems with these? Apparently they did not like that question...
That specific boiler was probably the most controversial one I could read about, but I still want to point at installer as the main reason for failures. Hence my need to ask questions.
They were also in the house for maybe 30 minutes, and asked 0 questions. I have every right to be leary no?
I don't know if my past experience with industrial systems is an accurate comparison, but although the modulating portion is where the most fuel savings and comfort levels are, that is also where most of the problems exist.
I would say that 95% of the heating problems we had were related to m-trac and related sensors , and were complex to troubleshoot. Parts cost a fortune and labor was time consuming.
All radiant tube, imfrared and conventional boilers almost always just worked and were extremely easy to troubleshoot on the rare occaision they did not. That is even more important in my house and could easily negate any fuel savings I might see.
I am not a pro but the pros that did come out had big problems trying to fix those systems, and they were only a couple of years old at the time and they were out every heating season and multiple times. The other systems I could always fix myself.
Is this an accurate comparison to what might happen in my house? No way to know. Is the simplicity of a non modulating system the way to go?
Again hard to say.
For what I am proposing here it will likely cost more to install a non modulating system, but I have great faith in Tekmar controls.
I also believe my biggest savings will be in getting this big old monster that's on its last legs out of here. Seems like proper sizing and eliminating that chimney is going to produce the biggest savings initially. Will modulation make that much more of a difference and at what cost long term?
This is why I'm still on the fence about the Cgi gv or mod con. Eventually I imagine mod con will be the only choice but for now....
The main thing I am trying to do is educate myself enough to know whether or not what someone proposes here I am comfortable with.
Kirkhj is offline
Old 05-20-2019, 06:11 PM   #12
Rewards Points: 986
I hear you. I spent a lot of time obsessing over all this stuff too. As far as the 20deg Delta T goes, I thinks that's something you shoot for but doesn't always happen. I almost never have anything close to one. I could tweak my pumps and stuff and maybe I will just because, but I basically keep my house around 70deg +/- 2deg 24 hours a day, year round, heat water with an indirect off the boiler as well as use propane for cooking and drying clothes and I haven't spent more than $1k year on propane yet.
Old 05-20-2019, 08:10 PM   #13
Xtrememtnbiker's Avatar
Trade: General Remodeling
Rewards Points: 342
I haven't tried to comprehend this thread but I read your post and it has made me want to save this and come back to it...
I'm going to build a house in several years and right now I live in a 2,500 sq ft house built in the 60's with oil heat and I spent $1,950 this winter on oil. That's with keeping the heat set at 65 throughout the day and having a program set to go down to 60 at night for about half of the winter.
Keep in mind I live in Richmond, VA. It's not exactly brutal here...
Xtrememtnbiker is offline
Old 05-20-2019, 08:30 PM   #14
Rewards Points: 986
Connecticut winters can suck. Im at around 1800sqft it finished space now. Last winter was sort of mild. Checked my tank last week and I was still at 50%. So well under $1k for this year. I fill up once a year and have a 1k gallon tank. I also have triple glazed windows, spray foam and a ton of air sealing which makes a big difference.
Old 05-20-2019, 08:44 PM   #15
Rewards Points: 342
My house has foil/paper type "insulation". There isn't even a band board at the end of the joists.
Looking forward to building and living in a more modern home that's detailed properly.
Old 05-21-2019, 03:22 PM   #16
Trade: Masonry
RE : sizing boiler,
Did you ever fail to maintain target temps with old furnace?
Use old boiler size as Max needed..
record gas usage while boiler is running for a + or - minus of 2% Btu input rating.....
Don't forget to add for very windy days.....
Again, seal up basement, VENT/supply combustion air, boiler and water heater mechanical room to exterior...
Insulate attics/roofs first, thermal window shades.
A breathable sealer on the masonry might reduce air changes....
make sure all gutter and drains, and drops are working, dry masonry has a higher R-value.
Maybe one or two Mini-split heat pumps for the family room upstairs as back up /zonal heating for wake- up/bedtime? or cheapest, a unvented open flame N.gas/L.P. wall furnace for cold spells?
A blower door test might find some easy to fix issues...
English/writing issues: Please define any trade terms at least once, preferably the first time used: see ModCon is a boiler that operates at partial ratings in a high efficiency condensing mode, that at full output runs in a non-condensing mode?
Old 05-21-2019, 06:36 PM   #17
Rewards Points: 986
Originally Posted by Fouthgeneration View Post
RE :
Condensing will be a result of return water temp and flu temp.
Old 05-21-2019, 08:42 PM   #18
Kirkhj's Avatar
Trade: Supervisor
Rewards Points: 18
Re: sizing boiler
I recorded input as 144 mbu. Rated input is 150. I ran it for a full 2 minutes to check that out. So calculating using that gives me an IBR of around 100. Rated at 104.
Always maintained or exceeded target temps. Max high limit setting of 170. First few winters high limit was 160 max. That extra 10 or 15 this last winter made a really big difference when it went beyond -40! At -42 with windchill in the -50's, this old beast kept up just fine! Brought the temp up in the house to 76 ( when I asked it to just to see)but when it was that cold it would almost never hit limit to make it to that 76. For whatever reason, I'm just not comfortable running this old boiler any higher than 170. Oh yea. The expansion tank became to small at anything over 160 and pressure started climbing fast. That's fixed now.
On the very coldest and windiest days we had this past abnormally cold winter, I adjusted temp up 5 beyond where we would normally keep the house just to see, and still managed to satisfy the thermostat...
Blower door test?
What would that be?
Attics are r 40.
Window coverings could be better.
Never thought about the dry masonry thing.
Mini split ac/heat pump I have actually been considering. Awesome stuff. Only issue is most of them do not supply heat at beyond -30, so electric fireplaces will do just fine for now. We have a couple of pretty nice ones. One looks Victorian and one hides the TV in the back on a motorized panel. They don't throw off much heat but sure are nice to have! Couple thousand Xtra btus can add up in the right spot.
The original wood fireplace has not been looked at yet, but would be an excellent place for that ng or maybe even wood pellet fireplace for sure. The masonry chiney for that still runs up and out the middle of the house, but there is no cold air coming out of that so time will tell. Most likely plugged up solid. Nice marble on the floor around that 1904 fireplace.
What's really stuck in my head is the thought that splitting up this single zone into 2 zones and running 2 delta t pumps on a p/s setup could really help (in the absence of a modulating system) I just keep thinking if I had been able to pump just a little more this past winter and get that delta at that sweet 20 and keep it there...lol. Yup. Obsessing is a good term for sure.
Kirkhj is offline
Energy Efficiency traviseh77 Electrical 6 04-10-2018 01:35 PM
Improving our efficiency Ohio painter Painting & Finish Work 27 08-21-2014 03:19 PM
New Guy: Energy Efficiency Contractor eecontractor New Member Introductions 1 02-22-2011 03:16 PM
Maximum efficiency framing crew size and methods UpNorth Framing 9 01-19-2011 03:17 PM
efficiency of Radiant versus convection air flashheatingand HVAC 8 04-15-2010 03:57 PM