HP Occasionally Kicks Into Heating Mode While Air Conditioner Is On - HVAC - Contractor Talk
Old 06-02-2011, 08:14 PM   #1
Happer's Avatar
Trade: Electrician
Arcoaire 3ton HP, sorry model and serial #'s to faded to see.
Been called out twice on this and have yet to narrow down anything as system is normal. Here goes...
When HP is in air conditioning mode, RV energizes on Cooling mode as normal. But sometimes while unit is in air conditioning mode, something causes system to start blowing warm air. (the HP is still running per tenant as I have asked them to check condenser) When I get there, I check pressure, they are in normal range, 72 L / 225h no pressure fluctuation . Condenser and evaporator coils are clean.
I have been looking at other options, as in bad RV coil, board, valve, t-stat thinking 24v is dropping off somewhere or RV is bad. But can't find anything while testing. I have checked wiring and voltages. Just wondering if anyone else out there has experienced this condition. And what I am missing
Thanks
Happer is offline
Old 06-02-2011, 09:17 PM   #2
MechAcc's Avatar
Trade: HVAC Service Technician --RSES CM-- NATE Certifie
Rewards Points: 150
Re: HP Occasionally Kicks Into Heating Mode While Air Conditioner Is On
You are listed as an electrician what experience do have on heat pumps? Could be an intermittent RVS solenoid or as you say electrical wiring. Connecting O terminal to R terminal will keep RVS energized without thermostat for troubleshooting. If problem disappears then you need to check thermostat wiring. If the problem continues with O connected to R and heat pump you can then do the same at thermostat. If problem goes away the problem is in the wiring. If it goes away it is in the thermostat. Many times with solid core wire there is always a possibility of a cracked wire that is causing intermittent problems.
MechAcc is offline
Old 06-03-2011, 07:19 AM   #3
Happer's Avatar
Trade: Electrician
Thanks Mech, my profile list electrician but also a Mech Cont, been one for over 20 years, Guess I need to change that profile so I don't get the heave- ho -what- for-discussion. I generally work on chillers but occasionally will look at residential air for friends and for my rental properties.
Anyway, I appreciate your response and will energize the valve as a means of troubleshooting.
Happer is offline
Old 06-03-2011, 03:06 PM   #4
pro user
kooltech's Avatar
Trade: HVAC contractor (owner)
Sometimes when the comp stops running due to overheating (motor quitting, refrigerant low, bad cap) they people will describe it as hot air as if the heater is on where in fact it's just ducts picking up heat from the attic and so on.
I would consider looking for a weak capacitor to the comp, bad start assist, contactor, outdoor motor, refrigerant etc. Anything which would cause the comp to open on IOL or fail to start.
I'd be sure a short isn't bringing on the heat strips.
kooltech is offline
Old 06-03-2011, 07:57 PM   #5
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,246
Probably a bad defrost sensor. The defrost board basically doesn't know if its in heating or cooling mode, it only knows to defrost when the defrost sensor.stat says its cold enough and the timer times out.
beenthere is offline
Old 06-03-2011, 08:43 PM   #6
flashheatingand's Avatar
Trade: H.v.a.c.
Rewards Points: 3,532
Mech, thanks for the heads up with energizing/ tying together O&R. I hope to remember that one.
http://www.37flash.com/
flashheatingand is offline
Old 06-03-2011, 08:59 PM   #7
Trade: H.v.a.c.
B.T., thats a good one to remember as well. I would suspect maybe a short to the elements, but that's just throwing a dart
Old 06-04-2011, 06:06 AM   #8
beenthere's Avatar
Trade: HVAC
Sometimes throwing a dart works pretty good. And over the internet, we're all throwing darts on limited info questions.
Old 06-04-2011, 08:08 AM   #9
pro user
kooltech's Avatar
Darts would surely short out the wiring.
kooltech is offline
Old 06-04-2011, 08:34 AM   #10
beenthere's Avatar
Trade: HVAC
LOL... My aim with darts isn't always good. I probably would end up hitting the condenser coil.
Old 06-19-2011, 12:32 PM   #11
Happer's Avatar
Trade: Electrician
Update...
Thanks for all the info. Being an intermittent problem I took a step back and started diagnosis all over again. It had been 4 days since it happened again so I loaded up the tools and headed over. The weather has been hotter than heck the last few weeks and I knew the system had been running almost constantly during the days, so this added to the question as why it only occurs every once in a blue moon. and as usual, it never happens when I got there.
I ruled out IOL after testing fan, cap and compressor. Next, I am thinking if the system continues to run, as she says, its either low voltage problem, circuit boards, or heat strip relays. I amped, ohmed, probed and tested everything in sight. Good thing the tenant wasn't hanging around otherwise she probably would have been tested to. Nothing.
So back to the air handler in the 120 degree attic. I get out the technical tools..my fingers...start moving wires around to see if everything is tight. CLIck Click click...okay on to something. Click..heat strips on, click they go off. Trace to circuit board. Just for kicks and giggles I jiggle the air handler..click click.
Pulling the CB, I noticed small piece of bare t-stat wire was laying under the board. Also small scorch marks on board where wire had been. Could this be it? Replaced board and so far its been 8 days and no call. I have no hypothesis to share on this..Maybe a fluke?
Happer is offline
Old 06-19-2011, 02:22 PM   #12
GettingBy's Avatar
Rewards Points: 6,486
If no failures for 8 days you can be 95% confident that the problem is gone if, before the fix, it failed once every 60 hours or so. If it failed less often then it's less than 95% confidence.
GettingBy is offline
Old 06-19-2011, 02:49 PM   #13
beenthere's Avatar
Trade: HVAC
You probably got it.
Old 06-19-2011, 06:05 PM   #14
Trade: H.v.a.c.
As B.T. said, you probably got it, but, possibly could have saved a few bucks by just fixing the bare wire...... Who knows, not there, and just throwing a light hearted jab. Thanks for the heads up, as all us us benefit from hearing the outcome.
Old 06-19-2011, 10:12 PM   #15
MechAcc's Avatar
Rewards Points: 150
Good find. Many times on intermittent problems we don't go the extra step to checking each and every connection.
MechAcc is offline
Electric Baseboard -vs- Electric In Floor Heating Keeyter General Discussion 13 03-09-2011 02:37 PM
how to do this heating system? roullette HVAC 3 03-26-2010 07:37 AM
Windows XP Mode in Windows 7! gideond Technology 9 05-14-2009 11:34 PM
Radiant floor heating in a large house KesslerDweller HVAC 2 02-21-2009 08:40 PM
Heating a metal building jray1969 HVAC 1 11-06-2008 05:57 PM