hey guys. Just seeing how you guys charge an ac system lets say a 16 seer r-22 system. Reason why i ask is that i went to school for ac but never went into the trade (stayed in the plumbing and heating side of it) i had a customer who had a problem with there ac unit so had a friend come over to fix it ( i knew what the problem was but i dont have the equiptment to evac the system) anyway when i was in school they though us how to charge a system using superheat. When i asked him about it he laughed and said he goes by his gauges (was a 10 seer so he went by 30+ degrees above amibent on the high side) So how do you guys charge a system
www.jpplumbingandheating.com
jpplumbing is offline
Old 07-12-2011, 08:59 PM   #2
flashheatingand's Avatar
Trade: H.v.a.c.
Rewards Points: 3,532
Re: How Do You Guys Charge A System
It depends on what the metering device is. If it's a txv, I go by sub-cool, if a metering device, super heat. If the literature isn't available, I go ten degree sub cool or super heat.
I do have a clamp on probe and like to keep the suction temp at about 55.
http://www.37flash.com/
flashheatingand is offline
Old 07-14-2011, 04:58 AM   #3
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,220
Super heat and sub cooling. I check both weather its a fixed metering device or a TXV. SH more important on fixed metering devices, SC more important on TXVs.
Charging by 30 over ambient is a great way to over charge a unit when it has a restriction in the circuit.
beenthere is offline
Old 07-14-2011, 09:31 PM   #4
30 year tech
hvac122's Avatar
Trade: hvac contractor
Ditto
hvac122 is offline
Old 07-15-2011, 07:07 AM   #5
MechAcc's Avatar
Trade: HVAC Service Technician --RSES CM-- NATE Certifie
Rewards Points: 150
First and always measure air flow. If the air flow isn't correct the charge will not be correct.
Subcooling method for txv system
Superheat method for flow restrictor system
MechAcc is offline
Old 07-31-2011, 09:52 PM   #6
Dr Heat
Dr Heat's Avatar
Trade: hvac
Rewards Points: 306
I charge based on the how much can you afford method then add 30 degrees supper sub-cooling txv divided by cfm over hvac delta tee.
actually I have a simple fool proof system for charging
1 clean condenser coil
2 check air flow
3 after condenser is dry use ether supper heat (fixed ) or sub-cooling (txv)
4 take an amp draw of the compressor
5 check for a 20 degree DT supply to return
Simple
Years ago I would look for a 60 to 70 pound back and a 225 to 275 head. but then years ago I sucked at this.
Dr Heat is offline
Old 07-31-2011, 09:56 PM   #7
beenthere's Avatar
Trade: HVAC
Is supper heat, anything like super heat?
LOL...
I hate when I make typos.
Old 08-02-2011, 06:34 PM   #8
Dr Heat
Dr Heat's Avatar
Trade: hvac
Rewards Points: 306
no supper heat is far more filling and tasty. Which is why I prefer it.
Dr Heat is offline
Hip Truss system Kent Whitten Framing 100 12-09-2012 07:15 PM
clemco easy load system and closed circuit blasting system goosesgarage Sandblasting 9 11-23-2010 12:41 AM
boiler system no heat rav1964 HVAC 18 12-06-2009 06:00 PM
Three level house boiler system TremblayElec HVAC 10 12-03-2009 10:56 PM
Getting your guys to "work together". J-Peffer Roofing 20 11-11-2008 12:42 AM