Calculating Combustion Air - HVAC - Contractor Talk
Old 03-08-2017, 09:03 PM   #1
3 Jacks 2 Nines
bwiab's Avatar
Trade: Wannabe Homebuilder
Rewards Points: 294
Looking at two 50 gallon power vent water heaters. Not direct vent so I need combustion air. Total BTU is 80,000 so if I follow the code
2009 IRC - Combustion air requirement = 80,000/1000*50CF = 4000cf.
I got 1920 cf in the utility room and 7500cf in the basement adjacent. So My understanding is that I only need two 100 square inch louvers in the wall separating the utility room and the basement. One up high and one down low. That sound right? Apreciate your insight!
bwiab is offline
Old 03-08-2017, 09:30 PM   #2
General Contractor
greg24k's Avatar
Rewards Points: 8,478
Re: Calculating Combustion Air
You need 2- 12x12 louvers one installed 12" from the ceiling and second installed 12" from the floor and that should do it.
greg24k is offline
The Following 2 Users Say Thank You to greg24k For This Useful Post:
belangerheating (03-11-2017), bwiab (03-08-2017)
Old 03-09-2017, 12:19 AM   #3
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,345
Why not use outside air to save $, a insulated 3" or 4" pipe to the sunny side of the house above the snow line,saving the cost of burning A.C. in the summer, Heated air in the winter?
A back up flapper vent on the doorway to the Hot water heater closet...
Do you have to adjust the jet or air flow at your altitude?
Fouthgeneration is offline
Old 03-09-2017, 05:23 AM   #4
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,204
That would be 2-100 sq in free area louvers. So as posted earlier, 2-12x12s.
beenthere is offline
Old 03-09-2017, 06:27 PM   #5
Trade: Masonry
You could build an insulated room around the HW heaters to isolate the waste heat by slowing the heat flow into the Air conditioned spaces during the A.C./dehumidifier seasons, closing any air returns or supplies from the A.C./furnace duct-work.
And of course reopening the ducts to spread out the "waste" heat in the heating season.
In modern super tight home, the suction of a radon gas blower, bath vent fans and appliances such as cloths dryers and Range hoods need to be considered regarding the creation of a negative draft that would cause exhaust gases to fill interior spaces....
Even a dry floor drain trap can allow the DVW roof stack to suck air out of confined basements. Or emit toxic sewer gases.
Question about workin on my own oil burner InterCounty HVAC 6 04-29-2013 12:05 AM
calculating crown spring angle Mrmac204 Finish Carpentry 12 12-26-2012 08:08 AM
Calculating Mud and Tape MasterBuilt Drywall 4 01-06-2011 08:08 PM
Combustion Air Calculations MechAcc HVAC 2 04-02-2010 05:42 PM