Securitron BPS 24-1 Over Voltage - Low Voltage - Contractor Talk
Old 05-28-2019, 11:41 AM   #1
Thatgy's Avatar
Trade: Low Voltage Security
Rewards Points: 8
Need some help please. I have two BPS 24-1's (24vdc) that have failed to 40vdc. This is the second replacement (same problem). The only thing they have in common is main voltage, which runs through a surge suppression outlet, and also a surge suppressor outlet strip. There also is a generator that is tested monthly. Voltage right at 120vac. Any thoughts as to what may be failing on the board for them to fail at 40V?
Thatgy is offline
Old 05-28-2019, 07:32 PM   #2
ABLE1's Avatar
Rewards Points: 1,274
Re: Securitron BPS 24-1 Over Voltage
Hello,
I am just a bit confused. Is the 40vdc a typo or are you somehow getting this 24vdc power supply pumped up to 40 Volts DC??
The units output is 24vdc. If you wanted 40vdc maybe you should
use a different unit.
Or am I missing something??
Thanks for posting here 1st. Please respond with some extra details such as what kind of business are you in and where are you located.
Les
ABLE1
ABLE1 is offline
Old 05-28-2019, 09:04 PM   #3
Contractor of the Month
Inner10's Avatar
Trade: Control Systems
Rewards Points: 5,076
Did it over charge the crap out of the battery? I've had power supplies output weird voltage but rarely with any significant current, just enough to show higher voltage on your meter.
They have a regulation circuit with an adjustable pot, so if that fails it could cause an over voltage. Put your meter on the battery leads and check the voltage, then adjust the pot up/down and see if the voltage changes.
Inner10 is offline
Old 05-29-2019, 02:58 PM   #4
Thatgy's Avatar
Rewards Points: 8
The power supply is "failing" the output is supposed to be 24vdc but the output is usually up around 38-40vdc.
They are power supplies used for card access door equipment.
Pot only varies voltage by a few tenths of a volt.
Fortunately they have a lifetime warranty but I don't really want to change them often, I will test after next generator test in a few weeks also.
Thanks
Thatgy is offline
Old 05-29-2019, 04:09 PM   #5
ABLE1's Avatar
Thanks
Ok, not a typo.
Is this voltage with no load?? This could be normally high without a load.
Then, if there is a load does it drop to 24vdc??
Also you do have two(2) ea. 12 volt Batteries in series = 24vdc??
What is the charging voltage?? Should be about 27vdc.
You say that there some surge protection on the 120vac source, is it properly grounded??
When you say it is failing. Do you know what has happened around
the time of the failure. Besides the generator test, can you monitor
the voltage during the switch over??
Last question, have you contacted Securitron to get their input??
BTW I have had very embarrassing moment when my
Fluke VOM had low battery and was reporting some really
weird readings.
Fresh batteries in the meter can make a difference.
Les
ABLE1
ABLE1 is offline