Need Help Sizing Main Beams For Pergola - Decks & Fencing - Contractor Talk
Old 12-16-2019, 01:26 AM   #1
RLH_CT's Avatar
Trade: GC/Finish work
Rewards Points: 60
Does anyone know of a beam sizing calculator that would tell me what's required to span 21' for a pergola? Redwood or doug fir beams and matching 8 x 8 posts secured to concrete patio with Simpson or equivalent knife plates. 3x8 x 12' cross members on top, client wants to grow wisteria over top which should weigh ~5 pounds/sf when mature.
Any chance a 6x12 would be enough? Really hoping not to need flitch plates for this! Thanks for direction and/or advice,
Rob
RLH_CT is offline
Old 12-16-2019, 11:29 AM   #2
hdavis's Avatar
Rewards Points: 1,046
Re: Need Help Sizing Main Beams For Pergola
Professional would be Woodworks Sizer program for PC.
You can also look up NDS values for the wood you're using and use a calculator like this one:
http://www.timbertoolbox.com/Calcs/beamcalc.htm
hdavis is offline
CityDecks (01-09-2020)
Old 12-16-2019, 07:10 PM   #3
Rooster Cogburn's Avatar
Trade: Master carpenter
Rewards Points: 336
Where can you even get redwood?
Rooster Cogburn is offline
Old 12-16-2019, 11:14 PM   #4
D-Construction's Avatar
Trade: General Contractor/Remodel
Rewards Points: 202
He's in North Cali., redwood is readily available in these parts.
D-Construction is offline
Old 12-17-2019, 12:59 PM   #5
VinylHanger's Avatar
Rewards Points: 12,876
We can get redwood same price or cheaper than cedar many times around here.
Sent from my SM-N975U using Tapatalk
VinylHanger is offline
The Following User Says Thank You to VinylHanger For This Useful Post:
Calidecks (12-18-2019)
Old 12-18-2019, 01:37 AM   #6
RLH_CT's Avatar
Rewards Points: 60
This version of the calculator seems to say that 6 x 12 redwood beams will work at 21 feet assuming I input the data correctly:
http://www.timbertoolbox.com/Calcs/ddsimplebeam.html
Very cool tool!
RLH_CT is offline
The Following User Says Thank You to RLH_CT For This Useful Post:
hdavis (12-18-2019)
Old 12-18-2019, 11:59 AM   #7
hdavis's Avatar
Very cool tool!
That one is for a set deflection. I'm guessing it's L/360, but I didn't see it documented on the page. Something like a pergola may only need L/240 or less.
hdavis is offline
Old 12-18-2019, 01:17 PM   #8
RLH_CT's Avatar
Rewards Points: 60
The calculated deflection with the projected weight was negligible - less than .3" over 252 inches. I could get up to more than 2,200 lbs per beam before getting to the .7" of deflection that would represent L/360 - so I will play with the beam sizes and load estimates to get ideas for the client.
RLH_CT is offline
hdavis (12-18-2019)
Old 12-18-2019, 08:47 PM   #9
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,723
Remember, You want it to work 30 years from NOW...
so one or two sizes greater then the minimum...
And draw it to scale to see if it "looks" safe.
Imagine a heavy growth of Ivy or grape vines with a freak snow load...
Fouthgeneration is offline
Old 12-18-2019, 11:22 PM   #10
hdavis's Avatar
Roof systems in houses are designed at L/240, so he's already above minimum. AG buildings may be L/180.
hdavis is offline
Old 12-20-2019, 08:53 PM   #11
Talking Head
EthanB's Avatar
Rewards Points: 434
Deflection due to self-weight is your main factor and that's not likely to show in any chart. I'd be concerned about a 6x12 over that span. We would probably go 14-16". Another option is to reduce the thickness to 4-5" to reduce the weight but that's an issue with most of our timber joinery. If you're using brackets it could work well.
Planer.....
EthanB is offline
The Following User Says Thank You to EthanB For This Useful Post:
asevereid (12-26-2019)
Old 12-21-2019, 01:53 AM   #12
RLH_CT's Avatar
Rewards Points: 60
I just bought some 18' 6 x 8' con heart redwood beams and after a couple weeks of air drying (in fall weather, so mostly dry but not that hot) they weighed less than 150 pounds - I was surprised at how light they were. Assuming that the weight is proportional, the 21' span would weigh 225-250'; the 12' long 3 x 8's horizontal rafters will each weigh ~75 lbs green and 55-60 or so when aged. Each beam will be carrying the equivalent of 6 "rafters", so another 300-400 lbs of stucture. Doesn't sound like a lot for a 6 x 12 to carry, but I appreciate the 'voice of experience', it's why I enjoy these forums.
RLH_CT is offline
Old 12-21-2019, 01:56 AM   #13
RLH_CT's Avatar
Rewards Points: 60
Ethan, what brackets would you suggest for these post->beam connections?
RLH_CT is offline
Old 12-25-2019, 09:42 PM   #14
Talking Head
EthanB's Avatar
Rewards Points: 434
Everything we do is either traditional pegged timber joinery or custom brackets. Simpson probably makes something that would work and be cheaper for your situation. We do all the engineering so custom is actually less for us.
Planer.....
EthanB is offline