Will A 100 Amp Breaker Work On This. - Electrical - Contractor Talk
Old 07-11-2015, 08:00 AM   #1
maninthesea's Avatar
Trade: High Pressure Air
Rewards Points: 30
I am trying to figure out what supply I need to tell my customer( who is an 800 mile plane ride away) they need to have ready for me to install their new machine. It is rated at 102full load amps 230v. Has a 15hp and a 20hp motor and some other small loads. The machine will not let both motors start at the same time.
My question is will a 100 amp supply breaker suffice? My electrical knowlage source will not be available till Monday. So I am asking here. My first two motor machine install.
I do have a 2014 NEC book if I knew were to look in it. Not that it applies in this case.
Thanks, Jim
maninthesea is offline
Old 07-11-2015, 09:37 AM   #2
GettingBy's Avatar
Rewards Points: 6,486
Re: Will A 100 Amp Breaker Work On This.
Have you seen
http://www.cooperindustries.com/cont...ion_Tables.pdf
GettingBy is offline
Old 07-11-2015, 10:27 AM   #3
Electrical Contractor
C'est Moi's Avatar
Trade: Electrical
Rewards Points: 550
The NEC requires us to use Table 430.250. Generally for 2 motors you need to add them together and and take 25% of the largest. The table shows 42 amps and 54 amps which comes to 109.5 with the 125%
54*1.25= 67.5
67.5+42 = 109.5
You stated that the motors won't start at the same time but I assume they will be running at the same time. It looks like you may need to go with 125 amp. Not sure what the smaller loads add up to be.
C'est Moi is offline
The Following User Says Thank You to C'est Moi For This Useful Post:
charimon (07-11-2015)
Old 07-11-2015, 10:57 AM   #4
GettingBy's Avatar
The NEC deals with motors, cables, switches, etc.
It never hit me before, but it seems the makers of these products who want happy customers will interpret the NEC for you, for free, so in some cases at least you don't have to buy books or take courses.
Old 07-11-2015, 03:41 PM   #5
Dave in Pa's Avatar
Trade: restoration/remodeling
Rewards Points: 1,272
So you sell something that you have no CLUE what is needed to run it?? Am I correct here? I just "might be" smarter than a 5th grader!
Dave in Pa is offline
The Following User Says Thank You to Dave in Pa For This Useful Post:
Speedy Petey (07-11-2015)
Old 07-11-2015, 04:11 PM   #6
CarpenterSFO's Avatar
Rewards Points: 2,044
If the manufacturer says that draw on full load is 102 amps, doesn't it make sense to have a circuit (and breaker) that will supply that, plus some headroom?
- Bob
CarpenterSFO is offline
Old 07-11-2015, 04:23 PM   #7
GettingBy's Avatar
And for a motor load I'd ask about the trip curve.
Old 07-11-2015, 04:25 PM   #8
John the Builder
SmallTownGuy's Avatar
Rewards Points: 6,114
Wonder if these guys know where Guam is, that the major source of income is tourism.
The military installations aren't much help - ain't much military that meshes with civilian needs. Lots of contractors there - all they do is military and then go hit the local massage parlors.
Max start load times 125% and go from there.
SmallTownGuy is offline
Old 07-11-2015, 06:00 PM   #9
Speedy Petey's Avatar
Trade: Electrical
Rewards Points: 1,244
Thanks, Jim
No, a 100A breaker is not good for a 102A load.
Wait until Monday to worry about this.
Please, leave the electrical work to those who know what they are doing.
And leave your code book in the office, or better yet give it to a sparky you know. You don't need it.
Speedy Petey is offline
Old 07-11-2015, 06:08 PM   #10
Seemed like a reasonable question to me. Maninthesea sells and installs certain equipment (big compressors?), and needs to inform the customer about the electrical requirements. His question is perfectly reasonable. Maybe it can't be answered on the information provided - that would be one answer.
- Bob
The Following 7 Users Say Thank You to CarpenterSFO For This Useful Post:
charimon (07-11-2015), GettingBy (07-12-2015), JT Wood (07-12-2015), Railman (07-11-2015), Rio (07-11-2015), rrk (07-11-2015), SmallTownGuy (07-12-2015)
Old 07-11-2015, 07:17 PM   #11
Trade: Electrical
If he's installing the equipment then he needs to be qualified to do the install. If he is also running the circuits to the equipment then he needs to be a qualified electrician as well. Based on the original questions the latter seems unlikely, so IMO he should NOT be doing the electrical branch circuit side of things. ESPECIALLY in a commercial/industrial setting.
The ONLY thing he needs to do is inform the client of the electrical specs, NOT how to wire it.
Old 07-11-2015, 08:21 PM   #12
Capra aegagrus
Tinstaafl's Avatar
Rewards Points: 474
The OP doesn't indicate whether he's planning to run any circuits or not. On the contrary, it sounds like the client is to arrange that and have the circuit(s) in place and ready to be connected. I think Jim's probably well enough qualified for that step.
Tinstaafl is offline
The Following 2 Users Say Thank You to Tinstaafl For This Useful Post:
CarpenterSFO (07-11-2015), rrk (07-12-2015)
Old 07-11-2015, 08:28 PM   #13
LRG WoodCrafting
Leo G's Avatar
Trade: Maker of Fine Sawdust
Rewards Points: 1,609
With a motor circuit usually the motor is protected by internal systems such as a motor starter.
Motor circuits are weird as the breaker can be setup for the wire current max or the inrush current. I've seen motors on 12 ga wire with 70amp breakers.
Sawdust Follows Me Everywhere
WWG1WGA
Carpenter by day.
Mad scientist by night.
http://lrgwood.com
Leo G is online now
Old 07-11-2015, 08:37 PM   #14
Contractor of the Month
Inner10's Avatar
Trade: Control Systems
Rewards Points: 5,074
He needs to tell the electrician what to install for the machine...whats the problem?
I think in this case the only person who can answer the question is the manufacturer.
Inner10 is offline
Red Adobe (07-11-2015)
Old 07-11-2015, 09:47 PM   #15
C'est Moi's Avatar
Trade: Electrical
Rewards Points: 550
Hopefully the electrician knows what to do.
Why is the mfg the only person that can answer the question. I believe I gave a code compliant answer and I must say that the mfg often give incorrect advise. I have run into that a few times.
Old 07-11-2015, 10:44 PM   #16
Red Adobe's Avatar
Trade: Metal Roofs, Sparky , Remodels and beer specialist
Rewards Points: 92
Another factor is wire length and what temperature conditions will be....
http://www.barr-thorp.com/wp-content...NEC-Tables.pdf
I'd go #2 copper and 125 amp
Red Adobe is offline
Old 07-12-2015, 06:00 AM   #17
Rewards Points: 30
Thanks guys. The MFR actuall answered my email on a Saturday which was great. His original email was a 100amp breaker might work but might trip every once in a while so recommended either going bigger or splitting he power supples. Then second email considered installation location and probability of voltage generally being low side recomended 125 or 150amps.
For the grumpy guys I have a better understanding than most on how electricity works, I was an electronic technician reactor operator in the navy. I forgot more than i remember. I use the NEC for wire size, & conduit size. I find no need to have an electrician run three wires & a ground from a power drop. Hate if you want. In the location this compressor is going I don't need any certifications nor NEC but I consider the NEC as a good guide. I do need to make sure I tell them what to have ready Becuase their "electrician" will generally be a guy from the PI that has a rudimentary knowlage.
Years ago I had the building owner fumeing mad at me Becuase I told them they needed 60 amp three phase and arrived to find single phase and refused to install. His reasoning was three wires = three phase deal with it.
The Following User Says Thank You to maninthesea For This Useful Post:
Railman (07-12-2015)
Old 07-12-2015, 09:35 AM   #18
GettingBy's Avatar
Then second email. . .recomended 125 or 150amps.
He should have said somewhere between 50A and 300A may work.
And he'd be right!
Sizing these things is supposed to be a matter of fact rather than a matter of opinion, the facts being dictated by physics and the constraints on what's allowed dictated by Codes.
WTF?
BTW, C'est Moi, I have to give you credit for showing how you got your answer.
Wiki gives #12 fusing at 5600A in 32 mS.
If a 70A breaker curve shows it tripping at less than this then it will protect the wire rather than the wire melting before the breaker trips.
Coolest Work Truck up for Sale Brimar Vehicles 23 02-01-2013 11:31 AM
Poor framing/concrete pad work from contractor netlinks Construction 10 10-26-2012 06:44 PM