Old 11-14-2018, 12:54 PM   #1
Occva's Avatar
Trade: Home Improvement
Rewards Points: 30
Had an old customer that wanted a vanity light changed out in a basement bath. I turned the switch off and removed the old light. When putting the new fixture mount on the neutral touched the ground and went zap. Tripped breaker 7. Thought that was strange. Got my volt meter out and checked hot wire with the switch on, read 120. Hot wire is breaker 8. Turned 7 back on and checked neutral, read 120.
This is 40's vintage. Just two wires. The ground is screwed to the back of the metal box.
How is this possible? It works fine.
Brought it to the home owners attention. We agreed to cap both wires and have my electrician look at it. He can't get there until next week.
Excuse me if I seem winded. I just got back from my French self defence class. Never ran so hard in my life!
Occva is offline
Old 11-14-2018, 01:47 PM   #2
I own stock in FotoMat!
480sparky's Avatar
Re: Two Circuits On One Wire
It's called a multi-wire branch circuit. And if your panel numbering is correct, it's not allowed on circuits 7 and 8. It's basically two circuits with one neutral and it can be overloaded.
Just let your Sparky handle it.
This post has been modified from its original version. It has been formatted to fit this screen and edited for content.
480sparky is offline
The Following 2 Users Say Thank You to 480sparky For This Useful Post:
Occva (11-14-2018), rselectric1 (11-14-2018)
Old 11-14-2018, 09:09 PM   #3
Renaissance Man
superseal's Avatar
Rewards Points: 5,846
Shared neutral...I got one at my house on 6/8 with a tie bar which I put on after making sparks when messing with it...vintage 40's home saving some scratch from the war effort.
supersealconstruction.com
superseal is offline
The Following User Says Thank You to superseal For This Useful Post:
Occva (11-14-2018)
Old 11-14-2018, 09:40 PM   #4
480sparky's Avatar
FYI: Opening a shared neutral can burn things up that are attached to the circuits.
The Following User Says Thank You to 480sparky For This Useful Post:
John Valdes (11-23-2018)
Old 11-15-2018, 07:54 PM   #5
back doors to hell put in
Irishslave's Avatar
Rewards Points: 1,314
It's why I don't like them. We've all seen what happens when a service neutral goes wonky. European system has no neutral everything is 240v and if I'm not mistaken 50 cps instead of 60
Irishslave is offline
The Following User Says Thank You to Irishslave For This Useful Post:
Tom M (02-11-2019)
Old 11-15-2018, 07:59 PM   #6
480sparky's Avatar
Too bad 'pert near every electrical service in the US is a MW circuit........
Old 11-15-2018, 08:13 PM   #7
Irishslave's Avatar
Never argue with an expert..........Thanks
Old 11-15-2018, 08:15 PM   #8
Capra aegagrus
Tinstaafl's Avatar
Rewards Points: 14
Ran into that when we bought our house. It was powered by a transformer at the neighbor's, a couple of hundred yards away. A heavy load on one side of the line would pop light bulbs on the other side.
POCO called it a "swinging neutral", and wound up giving us our very own transformer. But I had to fight my way through proving it to 5-6 different linemen and company reps, with my equipment and theirs. I still have a bit of a bad taste from that experience.
Tinstaafl is offline
Fouthgeneration (02-13-2019)
Old 11-17-2018, 07:43 PM   #9
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,953
Another reason to install as many appliances on 240 Volt circuits...
Air compressors, furnace motors, some kitchen appliances.
Suffered the loss of several motors and battery chargers on poorly balance 2-3 phase temp panels in the last ten years...
I am guessing both houses were wired by same sparky, and had systemically uneven loading of the half phase busses. plus under sized service wire
The current generation of lighting has to be changing actual % of electrical loads compared to legacy homes 20-30 years ago, reactive vs resistance, power factor and single pole vs dual pole supply/demand...
As Green energy State & federal mandates further devolve our Nation's Electrical Grid's day in day out performance, The need for constant monitoring of the homes power and other utilities actual values versus nominal numbers will soon be standard, IMHO.
Fouthgeneration is offline
Old 11-18-2018, 01:47 PM   #10
rescraft's Avatar
Trade: residential remodeling/construction
Rewards Points: 155
Always pigtail the neutrals in a MWBC
rescraft is offline
Old 12-16-2018, 06:38 AM   #11
caviepc's Avatar
Trade: electric
Rewards Points: 12
NEC requires multiwire circuits to be on 2 pole breaker so if one has a problem they both trip.
caviepc is offline
Old 12-16-2018, 10:26 AM   #12
480sparky's Avatar
The NEC only requires both circuits get turned off together. A 2-pole breaker (or 3-pole) is merely the simplest and easiest method.
Fouthgeneration (12-17-2018)
Old 02-11-2019, 05:01 PM   #13
Electrical Contractor
C'est Moi's Avatar
Trade: Electrical
Rewards Points: 550
The nec doesn't really require a dp breaker. You can use 2 sp breakers with a breaker tie. These can actually trip one circuit and not trip the other.
210.4(B)Disconnecting Means. Each multiwire branch circuit shall
be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch
circuit originates.
240.15(B) Circuit Breaker as Overcurrent Device. Circuit breakers
shall open all ungrounded conductors of the circuit both
manually and automatically unless otherwise permitted in
240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(1) Multiwire Branch Circuits. Individual single-pole circuit
breakers, with identified handle ties,
shall be permitted as the
protection for each ungrounded conductor of multiwire
branch circuits that serve only single-phase line-to-neutral
loads.
C'est Moi is offline
Old 02-11-2019, 06:11 PM   #14
caviepc's Avatar
Trade: electric
Rewards Points: 12
For the cost difference I can't be bothered with 2 Single pole breakers and tie handles.
caviepc is offline
Old 02-12-2019, 06:49 AM   #15
C'est Moi's Avatar
Trade: Electrical
Rewards Points: 550
I get that but I wanted to make sure others understood that it did not need to be a dp breaker. No biggie. I don't use multiwire branch circuit because of the afci issue and before that I didn't like them because when you loose a neutral you have problems.
Ken I know the feeder and the service conductors are multiwire branch circuit but I would like to minimize the issues if I can.
Down Idle wire broke on Rigid pressure washer Jas2012 Pressure Washing 8 06-19-2013 05:31 PM
3-way wiring- ceiling fan with remote for two-wire hookup hevnbnd Electrical 29 08-17-2009 10:28 PM