240V Circuit, But Only 140V Power - Electrical - Contractor Talk
Old 01-06-2008, 12:27 PM   #1
portlandamateur's Avatar
Hi guys, I have a question about my circuit breaker. Here's the story:
A week or so ago, my dryer stopped heating up. The dryer's been working fine until now, and it's the only thing on that circuit. No other major appliances have been introduced to the house. I tested a couple dryer parts with a multi-meter and couldn't find anything wrong. Then, I checked the outlet and only got 140V (should be 240). So, the tumber's running on the 140, but there's not enough juice for the heating element.
The house is about 35 yrs old, so I assume the breakers are also. I checked the oven's 240V outlet and measured 240V, so I'm confident I'm using the multi-meter correctly. I replaced the dryer's circuit breaker with a new GE breaker that was the same size/amps. The new breaker is in the same spot as the old one. This is a 2-pole double breaker.
I'm going to try switching the position of the breakers for the oven and dryer to see what happens. After that I'm out of ideas... Any suggestions?
portlandamateur is offline
Old 01-06-2008, 12:43 PM   #2
mdshunk's Avatar
Rewards Points: 2,002
Re: 240V Circuit, But Only 140V Power
Check the voltage right where the conductors connect to the breaker. If you have 240 there, then there's an issue with the branch circuit cable or possibly the dryer receptacle's internals.
mdshunk is offline
Old 01-06-2008, 01:08 PM   #3
what exactly do I need to touch to test that? The 2 wires coming from the breaker?
I don't think the problem is with the recepticle, I took the cover off and am touching the wires to test the voltage.
Also - I just put my dryer breaker into a different spot on the board. I put it where the oven breaker normally sits and still got the same 140 to the dryer outlet.
thanks for the help
Old 01-06-2008, 01:20 PM   #4
mdshunk's Avatar
Okey-dokey... you really need to put down the tools and step away from this situation, as you do not have the skill to effect this repair.
Call your electrician.
mdshunk is offline
Old 01-06-2008, 01:40 PM   #5
haha. you may be right - and that's probably what I'll do next.
I tested the voltage coming out of that breaker and got 240. I stripped back the wires at the outlet and still got 140.
From this, it seems that something's weird in the wires.... but that doesn't seem to make sense.
Even when I call an electrician, I'd like to know what the problem is... any ideas?
Old 01-06-2008, 01:44 PM   #6
ABLE1's Avatar
Rewards Points: 1,208
In a few should moments this was getting very scary to read. Hope he post back before he does something he will regret.
"Call your electrician"
ABLE1
ABLE1 is offline
Old 01-06-2008, 01:56 PM   #7
220/221's Avatar
Trade: electrician Phoenix AZ
The 240v circuit is 2 wires @ 120v each.
You have a bad connection SOMEWHERE.
GENERALLY the cable goes from the panel directly to the dryer. Through time and remodel things often get changed. You may have a junction somewhere, HOPEFULLY in a junction box.
Turn off the power, remove the receptacle and look at the terminals.
If there is nothing obvious, make sure it is a safe position and turn the power on.
Test each leg indididually to the ground. They should be appx 120v each. One will likely be less because of your bad connection.
Observe the cable at the recep. Does it match EXACTLY the cable at the panel? There could be a junction box somewhere if the dryer was relocated or if the cable was spliced somewhere for some reason.
Use your powers of deductive reasoning and be freaking careful.
In the mean time DO NOT USE THE DRYER. Your bad/burned connection wil get worse and may cause a fire.
Just because it's within code doesn't make it safe.
Just because it's against code doesn't make it unsafe.
220/221 is offline
Old 01-06-2008, 02:18 PM   #8
Service & Repairs
Magnettica's Avatar
Trade: Electrician
If you've got 240 at the CB, and 140 at the receptacle, I would suggest isolating the conductors from the receptacle and then check for 240 volts. That's what I would do.
If the problem persists, and if I had to guess, I would guess that somewhere along the line it had been tapped and used for a 120 volt circuit and maybe a switch is off. Something stupid like that.
Magnettica is offline
Old 01-06-2008, 02:22 PM   #9
Ok - i'm being careful and obviously not using the dryer. The recepticle itself is fine.
You're right. one wire has 110V or so, the other only has 60V. These look like the same wires as in the box. I doubt there's a junction, the box is only a couple feet from the dryer outlet. The problem must be in the one hot wire... Is it possible to just re-run the wires from the breaker to the dryer recepticle?
Here's a more general question... Where do the neutral wires go in all this? I understand they're connected to the buss bar, but why doesn't a 240V outlet have a hot, neutral, and ground like a 110V outlet?
Old 01-06-2008, 05:39 PM   #10
ABLE1's Avatar
Not knowing the answer or even asking the question is more of a reason to CALL AN ELECTRICIAN!!!!
No disrespect, but, are you looking to become an electrician and are looking to get some free education here??? You have a really bad connection and it needs to be corrected in a proper manner.
Others may help you here but it is not a good idea.
Les
ABLE1
ABLE1 is offline
Old 01-06-2008, 06:43 PM   #11
woah... relax. Thanks for the concern, i guess.
I'd be in big trouble if I was looking to become an electrician.
No, I'm just trying to get my dryer working again so my wife doesn't have to go to the laundromat. I've found a lot of helpful insights on this forum for a wide range of topics. Thanks to the advice here, I've narrowed down my problem to a single faulty wire. I'm going to continue with a little more research to find out how why there's no neutral wires in a 240V recepticle, then I probably will call a professional. I think my chances of getting over-billed or sold some BS for more work than necessary is probably a little less if I have a clue what I'm talking about - hence the questions I've posted here.
Old 01-06-2008, 07:05 PM   #12
mdshunk's Avatar
Yes, you are a poser homeowner. No doubt about it.
mdshunk is offline
Old 01-06-2008, 07:49 PM   #13
Rewards Points: 2,000
7 Hours and no one has pushed the ! ?
His name says it all.
neolitic is offline
Old 01-06-2008, 10:06 PM   #14
Service & Repairs
Magnettica's Avatar
Trade: Electrician
If his other double-pole circuits are producing 240 volts at the source, how the hell can he only be getting 60 volts to ground at the dryer receptacle??? That doesn't make sense!
Old 01-06-2008, 10:22 PM   #15
mdshunk's Avatar
Multiwire cable is real good for phantom voltage when using a DMM.
mdshunk is offline
Old 01-06-2008, 11:00 PM   #16
Moderator
Double-A's Avatar
Thanks for posting on ContractorTalk.com. The Moderators of this forum would prefer if you post Do It Yourself related topics on our sister site www.DIYChatroom.com
ContractorTalk.com is designed for professional contractor's to discuss issues and topics related to the construction and remodeling industries. Many of our professional contractors are also members at DIYChatroom.com and are looking forward to assist you with your needs.
Please take a moment to post your question at www.DIYChatroom.com If your not already a member of DIYChatroom.com you can sign up for a free account by going to http://www.diychatroom.com/register.php/
We apologize for any inconvenience that this may have caused. This thread has been closed.
New York Times, July 20, 2006
Double-A is offline
Affect of CFLs on power quality? Electric_Light Electrical 2 11-29-2007 03:56 AM
Need help with 240 circuit Elast Electrical 6 10-19-2007 03:03 PM
Power Rollers.... MarvinWilleyJr Painting & Finish Work 15 09-14-2007 09:12 PM
Solar Power Industry Dead In California w6ire Electrical 2 06-28-2007 08:57 AM
277v. on 240v. circuit ??? K2 Electrical 5 09-07-2006 06:19 PM