Reinforcing 8" Block Wall - Page 2 - Masonry - Contractor Talk
Old 02-22-2015, 05:26 PM   #21
concretemasonry's Avatar
Trade: Masonry consultant
Rewards Points: 2,960
Re: Reinforcing 8" Block Wall
fjn -
The moment at the base of the wall is only created if it is connected to the footing by grout and rebar. Otherwise it is simply supported wall that has horizontal resistance at the top and bottom. Usually the joists parallel to walls are blocked well between them for the first couple of spacings get the floor system to resist at the top of the wall.
If it is a wall on a strip footing with the typical basement floor cast over the footing, which is suggested/required in many ares, it is a simply supported wall that has no "moment" at the base and the moment of maximum stress in the wall is moved up to near the center of the wall area from the soil, so reinforcement can be required depending on the amount of retained soil. This stress is reduced somewhat by the vertical load from the walls and above floors and compressive strength of the masonry or concrete is usually not a factor of a home.
The bond beam on a masonry walls is just there to provide masonry continuity at the top of walls with no joists on it and a level area for bearing on all masonry walls.
In many areas where 12" masonry basements are used, a special filled top is used on the top course of the wall for good bearing and they can be grouted at down to 16" increments for anchor bolts. - A common historic term for those block is "FHAs" since they were required by the Federal Housing Authority (FHA).
Sorry for the engineering and code slant.
Dick
concretemasonry is offline
The Following 2 Users Say Thank You to concretemasonry For This Useful Post:
fjn (02-22-2015), jomama (02-23-2015)
Old 02-22-2015, 06:36 PM   #22
dom-mas's Avatar
Trade: masonry
Rewards Points: 626
I agree with concretemasonry (I think...not sure what a moment is in engineering). The major problem with block basements is soil pressure/hydrostatic pressure. reinforcement that doesn't join with the footing will still resist that soil pressure which is fairly low at the bottom near the footing. At the top where soil pressure is strongest the masonry should be tied in via the floor system so the area where it's going to be effected the most is in the middle and reinforcement every 4 cores should be plenty to deal with that. Personally I don't think horizontal re-enforcement is particularly necessary in this situation. Dead loads are pretty constant and fairly light
remember that the foundation has been doing it's job without ANY re-enforcement for 40-50 years
www.dominionmasonry.ca
dom-mas is offline
The Following User Says Thank You to dom-mas For This Useful Post:
jomama (02-23-2015)
Old 02-22-2015, 07:37 PM   #23
heavyc's Avatar
Trade: masonry
Rewards Points: 945
Originally Posted by fjn View Post
True,however,that gets you one bond beam. And that one is at the very top of the wall,more than likely above the unbalanced fill.....the place where it is needed the least and does the least good.
That's why you have vertical reinforcing?
Never seen horizontal reinforcing called out for at grade or an intermediate bond beam if you will at grade?
Although I would think that in conjuction with vertical reinforcing a continuous or more commonly called structural bond beam would provide more stability and continuity to the vertical reinforcing intention than none at all?
heavyc is offline
Old 02-22-2015, 08:16 PM   #24
PaulPrice's Avatar
Rewards Points: 226
I dont know that its not already re-inforced, I don't really know anything at this point, other than, from what I can see , it doesn't look bad, and would like to save some money by re-using the foundation.....I would say that the footing drain is a definate. I'd be hard pressed to build a new house on top of a potentially wet basement
The purpose for my inquiry, is simply to gain knowledge and prepare myself
PaulPrice is offline
Old 02-22-2015, 08:20 PM   #25
dom-mas's Avatar
Trade: masonry
Rewards Points: 626
The foundation was built outside of California 50 years ago. It doesn't have any reinforcement. Almost a guarantee
dom-mas is offline
slowsol (02-23-2015)
Old 02-22-2015, 08:28 PM   #26
heavyc's Avatar
Trade: masonry
Rewards Points: 945
PHOTO'S Would greatly aide in your request.
And I would also think the engineer
would be quite knowledgeable as that is his forte?
Seems a whole lot of brain power is being wasted? Without more information on your part?
As most some or all replies and input of knowledge may be mute?
heavyc is offline
Old 02-22-2015, 08:45 PM   #27
PaulPrice's Avatar
Rewards Points: 226
I'll get some photos, but the basement interior partitions have to be demoed first..... I was planning on using the structural engineer who does everything for me , for framing.... I don't know any masonry specific engineers, anyone got any suggestions.... As far as wasting knowledge/ input, I have nothing better to while my wife watches some award show, and don't incinveniance yourself on my behalf, but I do appreciate the advice
Old 02-23-2015, 12:23 AM   #28
Walraven's Avatar
Trade: carpenter/joiner
Rewards Points: 372
In my experiance with block retaining most situations require specific engineering from the footings up. Footing width,amount of bars in the cages, diameter of starters, centres of starters....etc etc.
As far as retro fitting reinforcing i know theres some cool new products out there as mentioned earlier they have been used over here abit for earthquake strengthening.
Walraven is offline
Old 02-23-2015, 05:18 AM   #29
dom-mas's Avatar
Trade: masonry
Rewards Points: 626
Figuring out steel requirements for a residential or light commercial block wall isn't all that tough. You need 0.002 of the gross cross section of the wall to be steel and for some to be horizontal and some to be vertical with a minimum of 1/3 in either direction.
In this situation it would be very difficult to add any horizontal steel and since the wall is already under built those steel requirements would change but for new work that is the method
dom-mas is offline
Old 02-23-2015, 10:58 AM   #30
fjn's Avatar
Trade: mason
Rewards Points: 11,202
Exactly,that is why belts work really good around our mid sections.
fjn is offline
concretemasonry (02-23-2015)
Old 02-23-2015, 11:10 AM   #31
fjn's Avatar
Trade: mason
This article sheds some additional light on the subject. Of particular interest is the chart depicting the unbalanced fill,which is always a concern. The soil type is also a very large factor,I.E. clay vs. sand or gravel.
http://www.masonryconstruction.com/I...68-1374431.pdf
fjn is offline
Old 02-23-2015, 12:29 PM   #32
heavyc's Avatar
Trade: masonry
Rewards Points: 945
FYI I prefer and use suspenders as I also need the vertical reinforcing they
provide.
heavyc is offline
Old 02-23-2015, 06:43 PM   #33
dom-mas's Avatar
Trade: masonry
Rewards Points: 626
Just because I'm an ass...another paper saying that joint reinforcement counts as horizontal reinforcement
dom-mas is offline
Old 02-23-2015, 07:02 PM   #34
Chief outhouse engineer
dakzaag's Avatar
Trade: mason
Rewards Points: 786
You guys are all messed up...
The main concern would be if the basement walls were exposed to fire or not. If the temp of the walls went over 600 F, the mortar and block will be ruined beyond repair and require replacement. I would basically assume any burn marks are over 600 and replace those sections.
If you're digging out the perimeter for a new footer drain, then by all means check out the wall and reinforce as needed. Pins and grout will do the most for the least and personally I would not get too concerned about drilling into the footer.
Helicoil could be added to the bed joints on the outside wall for extra measure. The manufacture probably has some data on tensile strength.
Get the deck back on before back fill. If it ain't broke, don't kid yourself into thinking you need to fix it.
D K & Sons
The maintenance schedule for brick
1. Stand back and say "man that looks nice!"
2. Repeat as often as needed.
dakzaag is offline
Old 02-23-2015, 07:20 PM   #35
heavyc's Avatar
Trade: masonry
Rewards Points: 945
I think if you read the 9th. post made after the starting thread. I most definitely made the statement your referring to? So I don't know that we're all messed up?
heavyc is offline
Old 02-23-2015, 07:30 PM   #36
muskoka guy's Avatar
Trade: framer/builder
Rewards Points: 558
If you wanted to install rebar into the wall and pour the wall solid, you would probably have to remove the top course or maybe two as these are usually poured solid or laid with semi solid block on the top course.
Unless the wall looks like it sustained very high heat, it will probably be fine if it has lasted 50 years in its present state. In Ontario, you could probably only be allowed to backfill about three feet on eight inch block. We use 12 inch block with rebar every hole, poured solid with concrete and we can only backfill about seven feet. Buttress walls on the inside are a great idea. As already stated, if the basement floor is poured a good portion up on the bottom block, it would help stop the bottom of the wall pushing in. Therefore rebar would help even if it cannot be drilled into the footing. If the floor isn't at least half way up the bottom block, the rebar will be fairly ineffective unless pinned to the footing somehow.
muskoka guy is offline
Old 02-24-2015, 09:08 AM   #37
dom-mas's Avatar
Trade: masonry
Rewards Points: 626
Yes it will. Soil (same as hydrostatic) pressure increases with height. There is little to no force at the bottom. and it would need to move all that soil to swing outward
dom-mas is offline
Old 02-24-2015, 10:28 AM   #38
fjn's Avatar
Trade: mason
Yes this is correct. One other important fact to keep in mind,the pressure exerted with an increase in height is exponential.Six feet of fill exerts considerably more than double the pressure of three feet of soil etc..
fjn is offline
concretemasonry (02-25-2015)
Old 02-25-2015, 06:45 AM   #39
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,797
Ask the local inspector if you have to retrofit reenforcement meet current codes
Cover it up before it freezes.... hope it isn't to late.....
Many CMU basements only work because the weight of house keeps both faces under compression. thus removing the weight of the superstructure will allow the basement walls to cave in.....even using 2x4 instead of 2x8 sillplates can allow the block roll more easily.
Worse case, its already cracked.... Hire a PRO, that knows masonry to inspect it.
Fouthgeneration is offline
Old 02-25-2015, 11:28 PM   #40
Rewards Points: 558
Why do they make us pin the bottom course to the footing if it has no benefit. Just asking.
Exterior wall covering options? bob_cntrctr Construction 8 02-25-2013 08:05 AM
Fastening 2x4's to Block Wall builder49 Masonry 11 12-28-2010 01:46 AM
Block Wall Footings, needed? K_Tile Masonry 22 12-06-2010 05:57 PM
any suggestions for this block retaining wall? ch0mpie Masonry 6 10-02-2009 03:06 PM
framing against block wall JohnHomeMatters Framing 12 10-01-2008 09:19 PM