Mortar Between Brick And Block Foundation Wall - Masonry - Contractor Talk
Old 07-30-2019, 09:55 PM   #1
Xtrememtnbiker's Avatar
Trade: General Remodeling
Rewards Points: 340
I'm just curious what any of your experience is with this. We just failed a foundation inspection because we didn't have mortar between the 4" block and 3 1/2" brick before the sill plate would be installed.
Our mason has never done this for us or anywhere else and we have never failed for it before in any of our jurisdictions. We do a lot more remodeling than additions and after some discussion we aren't sure if we have ever done an addition in this jurisdiction.
Any thoughts on it or knowledge of the code on it?
Xtrememtnbiker is offline
Old 07-31-2019, 08:04 AM   #2
tjbnwi's Avatar
Rewards Points: 1,834
Re: Mortar Between Brick And Block Foundation Wall
Picture please, from your written description I just don't get it.
I didn't think you could use 4" block for this type of situation, I recall 6" being the minimum.
tjbnwi is online now
Old 07-31-2019, 10:18 AM   #3
fjn's Avatar
Trade: mason
Rewards Points: 11,202
That 'space" between the brick and block is called a collar joint. If it is not filled with mortar,how are the anchor bolts secured ? Anyway,here is a connection to an article about those joints. As it states,collar joints are one of the least understood topics in masonry. Also,please note,increasing the width to 1" allows for easier filling than holding to the nominal dimension which in many instances yields a collar joint of 5/8|" - 3/4".
My take,yes,they should be conscientiously filled rather than the usual hit or miss approach. If not filled intentionally,they should be built as a drainage plane.
https://www.concreteconstruction.net...ollar-joints_o
fjn is offline
The Following 3 Users Say Thank You to fjn For This Useful Post:
Fouthgeneration (08-01-2019), Seven-Delta-FortyOne (08-08-2019), stuart45 (08-01-2019)
Old 07-31-2019, 03:37 PM   #4
NYCB's Avatar
Trade: Concrete/Masonry
Rewards Points: 682
I had to google it.
I've never heard of one or seen one spec'd on a foundation plan.
What is the purpose of them?
NYCB is offline
Old 07-31-2019, 04:51 PM   #5
hdavis's Avatar
Rewards Points: 2,362
I'm still trying to figure this one out. You installed the sill plate before filling? Or, the foundation was inspected and you hadn't filled the gap?
hdavis is online now
Old 07-31-2019, 05:40 PM   #6
fjn's Avatar
Trade: mason
Originally Posted by NYCB View Post
I had to google it.
Well,as the article states,collar joints are one of the most misunderstood components of a masonry wall. As a result,architects don't know what to do with them,maybe never give them a thought. However,a brick and block wall is commonly thought of and referred to as a barrier wall. Barrier to what ? Water ! Hence,as the article states,if no thought is given them,mortar fins compromise the partially / improperly filled joint and create a environment to trap water and it's resulting problems. So,the gist of the article is about how to properly design and fill the collar joint. As brought out,mortar is not fluid enough to accomplish that task and "slushing" the collar joint in a attempt to fill it is futile and detrimental.
Also,as I questioned in my first post how the heck do you affix anchor bolts with a brick wall with 4 " block if you don't fill the collar joint ? I can easily see how this job was red tagged. I'd tag it myself if I was inspecting.
fjn is offline
Old 07-31-2019, 06:02 PM   #7
NYCB's Avatar
Rewards Points: 682
I mean what is the use of them?
If you have a block wall, why is there a course of brick on the top before the sill plate.
Wouldn't you be better off with half height block for that extra height?
NYCB is offline
Old 07-31-2019, 06:10 PM   #8
fjn's Avatar
Trade: mason
I think you misunderstood him. His 8 " foundation wall is comprised of a 3 5/8" brick and a 4 " concrete block. The mason never filled the longitudinal /"collar" joint between the wythes. The ship has sailed to fill it after the fact because if the joint is less than 1-2 " and meticulously kept free and open,the mortar fins will negate the chance to grout them solid. It is NOT a 8" block foundation. It is a composite wall. Meaning brick with block back up. Also,the inspector is probably really concerned with anchor bolt placement.
fjn is offline
Old 07-31-2019, 09:02 PM   #9
Rewards Points: 340
Our standard foundation in this are is an 8" block below grade and a 4" block with 3 1/2" brick above grade. As fjn stated, it is the collar joint I was referring to. I just didn't know that's what it was called.
Yes, collar joint. My mason has been laying brick for longer than I have been alive and he's never filled a collar joint at the top of the wall.
Sill plate wasn't installed yet, I just mentioned it only to help with the description of what part of the foundation wall I was talking about. Maybe it was more confusing cause of that. Inspection happened with the collar joint not being filled.
Our anchor bolts are in the core of the 4" block. It's really stupid according to my mason and the inspector. They both said it used to be 18" long bolts that hooked under the second row of block and were between the brick and the block. Several years back we had to move them to the core of the 4" block and it's a pain because it's way off center of the sill plate so as you tighten the nut on the bolts it wants to rock up the outside of the sill sometimes.
The Following User Says Thank You to Xtrememtnbiker For This Useful Post:
hdavis (07-31-2019)
Old 07-31-2019, 10:29 PM   #10
hdavis's Avatar
So what's the fix, cut the brick off and redo? Use the grout that's used for grouting in machinery? Pump in cement with acrylic admix? Vinyl cement patch? Epoxy fill the whole thing?
Old 08-01-2019, 01:05 AM   #11
stuart45's Avatar
Trade: Brickwork
Rewards Points: 1,248
https://www.masonry.org.uk/downloads...-buildability/
Unfortunately BRE charge you 12 to read their full report. They charge for everything since they were privatised.
stuart45 is offline
The Following User Says Thank You to stuart45 For This Useful Post:
fjn (08-01-2019)
Old 08-01-2019, 01:23 AM   #12
Fouthgeneration's Avatar
Trade: Masonry
Rewards Points: 9,403
I can't imagine any house built on just an 8" wide brick and 4" CMU back up wythe anymore.....horrible detail for vermin resistance, mouse/rat proofing.
Top course should be a bond beam too, even the 4" silliness. make sure you use Grout-able large Two hole 4" units, sawn California style cheaper then bough-ten...
It doesn't meet any E code in North America.... or provide a working rain screen, without water proofing the CMUs and installing damproof flashing at Grade AND at the beginning of the brick ledge.
add a grouted bond beam to secure an angle iron brick ledge to, a 5-6" angle for insulation space,
is some real money and tension loads on the anchor bolts.....
A korbel 8-12" block is much better then a angle that will eventually rust away/fail....
Lay 10, 12 or 14" CMUs with a bond beam and smaller block starting there (6"-8") with ~2" foam and 3/4" air space.
Using sheathing mounted insulation layers of 1.5 to 3" to achieve high R values in-spite of studs bridging the wall cavity, might require a wider sole plate to protect the insulation from vermin interference / degradation.
Old school, lay some grout stop in the last block bed joint, fill with grout AFTER tarring the block's exterior face above the brick ledge start,( I always tarred the FLAT too, as a C.J. and dampproof layer. for rising damp/water vapour.
1/2 Anchor bolts in the re-barred and grouted CMU cells, long enough to reach down two courses of block when installed ~4' apart, AND 3/8" Shorter anchor bolts in the brick every 4' to 5'-4" or so to keep the plate flat. Retighten anchor bolt nuts when dry wall is hung....wood framing is dried out...
Old days pre super grouted basements all cross webs on first two and last two course were to be spread with mortar for add connections between the two block face shells..... and wire in the first an last courses always for more strength.
In California, post ~1950s pre-seismic tested brick anchors era, all above grade brick "veneer" was grouted solid to the back up block or tile. and usually the bond was checked with test panels..... the "collar joint created by the Brick and Blocks wythes adjoining faces.
Wouldn't be very pretty in wetter climes.
Fouthgeneration is offline
The Following 2 Users Say Thank You to Fouthgeneration For This Useful Post:
fjn (08-01-2019), JBM (08-08-2019)
Old 08-01-2019, 09:28 AM   #13
fjn's Avatar
Trade: mason
Yes, collar joint. My mason has been laying brick for longer than I have been alive and he's never filled a collar joint at the top of the wall. QUOTE
I love it when I catch any tradesman doing something the incorrect way and they tell me " I've got over 20-30 40 years experience ". I say no you don't you have 1 years worth of experience replicated 20-40 times.
If he has been doing it all those years,I hate to bust his bubble,he has been doing it incorrectly all those years.
Here is an article talking about the cost of unfilled mortar joints. While it mainly pertains to head and bed joints,all joints should be properly and completely filled.
https://www.concreteconstruction.net...illed-joints_o
fjn is offline
Old 08-01-2019, 09:45 AM   #14
fjn's Avatar
Trade: mason
[QUOTE=Fouthgeneration;
Additionally,over here (Chicago area) The two courses directly below bearing points ( joists and steel beam pockets) needed to be either solid block or grouted solid !
fjn is offline
Old 08-01-2019, 09:51 AM   #15
fjn's Avatar
Trade: mason
Good abstract, spells it out,leaves nothing to the imagination.
fjn is offline
Old 08-01-2019, 05:19 PM   #16
NYCB's Avatar
Rewards Points: 682
That makes more sense.
I read foundation so I just assumed it wouldn't have brick below grade.
I didn't know walls like that were still a thing, every time I've seen real brick its been a veneer and built on a brick ledge.
NYCB is offline
The Following User Says Thank You to NYCB For This Useful Post:
fjn (08-01-2019)
Old 08-01-2019, 11:24 PM   #17
stuart45's Avatar
Trade: Brickwork
https://www.contractortalk.com/attac...hpxt2dempm.jpg
Bricks used to be used in foundations all the time here, although it's normally blocks now.
They still can be used below ground as long as they have the correct frost rating.
I used some engineering bricks on an extension I did at home as I was given the bricks.
stuart45 is offline
The Following 2 Users Say Thank You to stuart45 For This Useful Post:
fjn (08-02-2019), Fouthgeneration (08-02-2019)
Old 08-01-2019, 11:40 PM   #18
Trade: Masonry
I've moved the face of 8" cmu footings out to the "ashlar" line, the face of veneer masonry to eliminate the need for an ADDED on brick ledge, usually ending up with Korbels facing inward to carry the SOG for the garage.
The stepped out CMUs making the basement ~8" wider and longer at a tiny cost of planning and materials, = a ~52' square foot of floor for a bath or closet.
Currently the insulation requirements don't favor 8" wide foundation IMHO, especially on Masonry veneered homes.
A brick panel with a top filled collar joint should have vents installed just below the collar grout, if above grade of course.
Old 08-02-2019, 12:15 AM   #19
Trade: Masonry
Most homes in the USA are subject to insect attack of the wood that is with in 18" of the soil...
and almost all homes should be above the 100 year rain event of 5-10 inches of rain in 6-12 hours flooding.... thus the need for ~18" or more of finished basement wall, that has insulation and a working Rain-screen below the Wood of the sill plate, (in a wood framed home).
= a first floor at 28-36" above finished grade, except at the front door and Patio door(s)
On grade Frank Lloyd Wright style homes are silly money pits IMHO.
Old 08-02-2019, 06:06 AM   #20
NYCB's Avatar
Rewards Points: 682
I avoid laying block like the plague, but when I end up getting one it almost always calls for 10 or 12" block on a new foundation.
The only time I use 8" is on stuff like additions to match existing, or garage walls.
NYCB is offline
The Following 2 Users Say Thank You to NYCB For This Useful Post: