Goodman Furnace - Page 2 - HVAC Picture Post - Contractor Talk
Goodman Furnace
Old 11-27-2011, 11:31 PM   #21
Dr Heat
Dr Heat's Avatar
Trade: hvac
Rewards Points: 306
Re: Goodman Furnace
Originally Posted by Ken Good View Post
Gas pressure at the meter should be no greater than 9" WC for residental applications. Call the utility in your area and they will replace the regulator. As to installers not reading the manual, this is the number one reason for rejects and additonal costs.
I must have missed it did the op say Natural Gas or Propane Gas?
Dr Heat is offline
Old 06-08-2012, 04:34 PM   #22
ral62's Avatar
Trade: HVAC
Rewards Points: 41
Re: Goodman Furnace
Look on the placard inside the furnace. It will tell you the inlet range and the outlet range. I may be wrong but the inlet I think should not be over 11.5 inches and outlet of 3.5
ral62 is offline
Old 10-20-2012, 02:51 PM   #23
Atticus Finch's Avatar
Rewards Points: 25
Re: Goodman Furnace
My guy says you've got a cracked heat exchanger. Or induction fan is out. Assuming the proofing system on the fan checks ok, the heat exchanger is cracked. DANGEROUS! Expensive but necessary fix!
Atticus Finch is offline
need furnace expert - Goodman furnace DMC HVAC 22 02-19-2009 01:24 PM
Goodman 80% furnace brand new won't start Hguy HVAC 21 03-28-2008 11:05 PM
Goodman Furnace stopped running ColdInCO HVAC 1 01-22-2008 10:36 PM
Goodman 80% furnace won't start with side cover on rlelliott HVAC 7 12-09-2007 12:42 AM