Simpson Tie Downs - Spalling - General Discussion - Contractor Talk
Old 08-15-2019, 09:32 AM   #1
Gijsbrand's Avatar
Trade: Plumbing
Rewards Points: 40
Hi,
Should spalled areas at the straps (STHD14) be repaired? And how? And by whom? (new house)
https://drive.google.com/open?id=1-T...X5P-OhVeG69rl0
THANKS
Gijsbrand is offline
Old 08-15-2019, 10:35 AM   #2
TimNJ's Avatar
Rewards Points: 5,672
Re: Simpson Tie Downs - Spalling
I wouldn't leave it looking like that.
TimNJ is offline
Old 08-15-2019, 11:02 AM   #3
Fire up the BBQ
griz's Avatar
Rewards Points: 578
there are a number of masonry patching compounds available.
repaired by the gc or who ever installed it.
griz is online now
fjn (08-16-2019)
Old 08-16-2019, 06:46 PM   #4
fjn's Avatar
Trade: mason
Rewards Points: 11,202
Looks like placed way to close to edge.
fjn is offline
The Following 2 Users Say Thank You to fjn For This Useful Post:
greg24k (08-19-2019), TheConstruct (08-16-2019)
Old 08-19-2019, 03:49 PM   #5
sunkist's Avatar
Trade: builder fl cbc
Rewards Points: 890
What Simpson # is that ?, I am not sure what is holding that in place,
Still "Shakin" the tree boss
sunkist is offline
Old 08-19-2019, 05:03 PM   #6
GC/carpenter
Calidecks's Avatar
Rewards Points: 3,814
You need to check the simpson ESR and see what the minimum concrete on each side is.
https://icc-es.org/wp-content/upload...y/ESR-3050.pdf
See figure 6
Mike.
_______________
Calidecks is online now
B.D.R. (08-19-2019), fjn (08-20-2019), greg24k (08-19-2019)
Old 08-19-2019, 05:05 PM   #7
GC/carpenter
Calidecks's Avatar
Actually looking at your picture that doesn't look like a column be it looks like a Column cap placed upside down.
Or a column base upside down.
Looks like one of these upside-down
Mike.
_______________
greg24k (08-20-2019)
Old 08-19-2019, 05:31 PM   #8
Dan_Watson's Avatar
Rewards Points: 2,748
It is a Simpson Strap, maybe the STHD14, but I think it is cut and maybe installed upside down?
Right under the large hole it says Top of SM1, which is the Simpson Strap holder.
Simpson Tie Downs - Spalling-20190815_075404.jpg   Simpson Tie Downs - Spalling-cf_sthd_instill_ill_inst_corner_cy.jpeg
Dan_Watson is offline
Old 08-19-2019, 06:35 PM   #9
JFM constr's Avatar
Trade: remodel,finish&trim
Rewards Points: 2,250
that is to funny . sometimes i see hardware installed just"because" .with no actual purpose in it's use .this could be such a situation .anyhow OP has seen it and now he owns it . fix it . not referring to covering it up either .
JFM constr is online now
Old 08-19-2019, 06:37 PM   #10
Gijsbrand's Avatar
Trade: Plumbing
Rewards Points: 40
Thanks for all replies and suggestions.
This is what Simpson told me:
The STHD14 Strap-Tie Holdowns can have a spall up to 4" and still maintain its full load capacity, a spall greater than 4" will cause a reduced capacity though. In order to evaluate any spalls greater than 4", we would need to get the information regarding the size of the spall as well as the demand load expected from the strap by the Engineer of Record. All spalls need to be repaired with a grout to provide weather protection or the strap could corrode. StrapMateŽ Strap Holders are specifically designed to set the STHD straps to minimize the possibility of spalling, they do not guarantee that spalls won't happen, but th chance is reduced substantially.
Home is just 3 months old, with 1 yr warranty. Builder is not going to repair the spalling though. It is indeed the STHD14, no embedded columns. More pictures:
20190815_072021
Old 08-19-2019, 06:46 PM   #11
JFM constr's Avatar
I do have a question .Were they installed properly .For a hold down it would seem a lot of room for lateral movement of the building .
Old 08-19-2019, 06:55 PM   #12
Dan_Watson's Avatar
I see now, looks like it was installed too low?
Old 08-20-2019, 12:27 AM   #13
Dirtywhiteboy's Avatar
Rewards Points: 13,004
They were installed wrong! There is a orange angled bracket that simson sells to mount it to the form that angles the strap into the slab to prevent that. We had a big mess out here because of that on hundreds of homes.
Dirtywhiteboy is offline
Old 08-20-2019, 04:27 AM   #14
General Contractor
greg24k's Avatar
Rewards Points: 8,478
They were installed wrong, this would never fly, and it's doomed for failure.
greg24k is offline
Old 08-20-2019, 09:37 AM   #15
Gijsbrand's Avatar
Trade: Plumbing
Rewards Points: 40
They may not necessarily be installed incorrectly. The strap MAY be installed with the SM1 (StrapMate).
What bothers me is that Simpson specifically says in their reference guides that any exposed metal (G90 galvanized, low resistance to corrosion) should be protected against corrosion. Builder knowingly left it exposed. Furthermore, concrete that has spalled like this, is susceptible to further deterioration, and aesthetically looks like crap.
I will talk with the code/building inspector and see what he has to say.
From Simpson application guide:
STHD straps may be installed over 1⁄2" maximum wood structural panel sheathing. Installing STHD with StrapMateŽ strap holder reduces the possibility of concrete spalling.
Strap may be bent one full cycle (bent horizontal 90° then bent vertical) to aid wall placement, but may cause spalling behind the strap. If the spall is 1" or less, measured from the embedment line to the bottom of the spall, full loads apply. 1" to 4" spalls for LSTHD8 achieve 0.9 times table loads. STHD10 and STHD14 achieve full load for spalls less than 4". Any portion of the strap left exposed should be protected against corrosion.
Old 08-20-2019, 09:47 AM   #16
Gijsbrand's Avatar
Trade: Plumbing
Rewards Points: 40
And builder is blaming it on the framers, pulling tension on straps causing the spalling, but in pictures it is obvious the spalling is already there after pouring foundation, before framing...
Old 08-20-2019, 09:49 AM   #17
sunkist's Avatar
Rewards Points: 890
20190815_072021
Well that looks like a sh#t show in a couple of pics
, doomed to fail.
sunkist is offline
The Following User Says Thank You to sunkist For This Useful Post:
griz (08-20-2019)
Old 08-20-2019, 09:59 AM   #18
Gijsbrand's Avatar
Trade: Plumbing
Rewards Points: 40
ICC-ES Evaluation Report ESR-2920:
Strap-style hold-downs and purlin anchors must be installed with the minimum embedment depth, le, noted in Table 1 through Table 5 of this report. The strap may be bent one full cycle (bent horizontally 90 degrees then bent vertically) to aid wall placement. Bending of the installed strap may cause concrete spalling behind the strap. If the spall is 1 inch (25 mm) or less, measured from the embedment line to the bottom of the spall, full loads apply. Any portion of the strap left exposed must be protected against corrosion by providing weather protection complying with 2018 IBC Section 1402.2 (2015, 2012, 2009 and 2006 IBC Section 1403.2) or IRC Section R703.
Old 08-20-2019, 11:28 AM   #19
JFM constr's Avatar
1st and second photo .that gap between strap and foundation seems wrong . were they not designed or placed to attach to framing and not the siding .
Old 08-20-2019, 11:42 AM   #20
GC/carpenter
Calidecks's Avatar
I believe they are to be attached to the shear into the framing.
Mike.
_______________
Dirtywhiteboy (08-20-2019)