Re: Foundation Vents In Addition
Originally Posted by greg24k View Post
If you take out the foundation vents you need mechanical ventilation.
R408.3 Unvented crawl space.
Ventilation openings in under-floor spaces specified in Sections R408.1 and R408.2
shall not be required where the following items are provided:
1. Exposed earth is covered with a continuous Class I vapor retarder. Joints of the vapor retarder shall overlap by 6 inches (152 mm) and shall be sealed or taped. The edges of the vapor retarder shall extend not less than 6 inches (152 mm) up the stem wall and shall be attached and sealed to the stem wall or insulation.
2. One of the following is provided for the under-floor space:
2.1. Continuously operated mechanical exhaust ventilation at a rate equal to 1 cubic
foot per minute (0.47 L/s) for each 50 square feet (4.7 m2) of crawl space floor area, including an air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.11 of this code.
2.2. Conditioned air supply sized to deliver at a rate equal to 1 cubic foot per minute
(0.47 L/s) for each 50 square feet (4.7 m2) of under-floor area, including a return air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.11 of this code.
I am not sure if code addresses crawl space liners but it made a big difference in my crawl space. I have ductwork in my crawl space and it would condensate in the humid summer months. After the crawl space liner and closing up the vents i have no condensation on my ducts in the summer. I never did understand letting warm moist air into a cool crawl space. Do a search on crawl space liners and it makes sense.
nicko
"Quality work for those who know the difference"
nickko is offline
Old 04-29-2019, 06:41 PM   #22
Always Learning
overanalyze's Avatar
Trade: Builder/Remodeler
Rewards Points: 702
Originally Posted by builditguy View Post
What we do for the most part.
We put down visqueen, then pour concrete in all crawlspaces. We only pour it about 3" thick and it only gets a bull float finish.
Then spray foam the walls. Lately they also get a layer of fiberglass blanket over the top, due to code.
I think the blanket covering the foam is due to the flame spread of the spray foam. My understanding was it wasn't required if there wasn't an ignition source in the space like a furnace or gas line but maybe I interpreted it wrong.
overanalyze is offline
Old 05-01-2019, 06:28 AM   #23
builditguy's Avatar
Rewards Points: 1,322
I believe you are right about the flame spread. I don't know about the ignition source. The spray foam company I use won't do, only foam.
Could be their own company policy, to charge a little more, or to protect them from liability.
I know a homeowner sued the GC on a house, a couple years ago. All of the subs were included in the suit. They were one of the only companies that were found innocent, because they had done everything by the book. Maybe they are gun shy now.
builditguy is offline
The Following User Says Thank You to builditguy For This Useful Post:
overanalyze (05-01-2019)
Crawlspace access to addition from main house jjperry84 Construction 10 03-02-2017 02:59 PM
Retrofit Foundation Vents? miillersickness Carpentry 0 12-26-2012 04:26 PM
Provisions for future concrete slab addition txgencon Concrete & Paving 2 03-30-2011 08:11 PM
Waterproofing A Foundation Wall With No Access dcbuilder Construction 16 01-31-2011 06:52 PM
Truss uplift or foundation movement NailBender2 Carpentry 6 01-05-2011 05:22 PM