Do vents have to go right above the drain? Or can they be relocated a foot or so off of the drain?
I have a the drain come from the ground and then go into a san. tee then the vent. I want to take the vent from the san. tee then direct it about a foot off to the side of the top of the san. tee. |
Future Mod...
Trade: Master Plumber
Re: Vents And Location
yea as long as you dont use 90's untill your above flood rim level....you can use 45's though
Trade: HVAC
Re: Vents And Location |
Trade: HVAC
Looking in my book it is the "edge of the fixture in which the water drains"
So does that mean I can't use a 1/4 bend underneath the sink? (this is a kitchen sink drain. |
Electro-Mech. Contr.
Trade: Mechanical Contractor
You have three feet from where the fixture trap ties into the branch line to have your vent connection. But any offsets below the flood level rim of the sink have to be less than 1/4 bends as the other poster mentioned.
"Injustice anywhere is a threat to justice everywhere" mlk 100% Union and Proud of It |
Trade: Plumber
My state allows up to 5' for a 1-1/2" traps vent, Pyro, you should have a chart in your code book.
You should have a code book for your course, if not...GET ONE! |
The Grand Wazoo
Beyond 5 feet at a 1/4" per foot the trap is wet vented. Chicago code allows five feet max, no matter the pipe size.
Trade: Plumber
Ours is simple.
Diameter X 2 + 2 = the linear max in feet the vent can be connected. 1-1/2" is 5, 2 is 6, 3 is 8...etc. Wet vents are stricktly 2" run from the lav drain and connected within the required distance for the other 2 bath fixtures. UPC has a chart that allows much less distance than my state does. |