Trade: Excavation
Underground Diesel Tank
I have a client that has a 500 gal fiberglass diesel tank (supplies an indoor backup generator) that he wants me to uncover and investigate for leakage. He also wants me to disconnect the supply and return lines and pressure test them. Any advice on best way to do this pressure test? Anything else to look out for? Thanks
Duff |
Future Mod...
Trade: Master Plumber
Re: Underground Diesel Tank
what kind of lines? soft copper? if so get 2 flare X pipe thread couplings and put a gauge on one end and cap the other end... once you have tested the one side switch it over to the other.....all the oil fired appliances around here are supplied in 3/8 soft copper
The Grand Wazoo
Check your local requirements, here in Illinois you have to have an EPA certification to do any excavating of a fuel container, and to have sufficient equipment to handle an accidental rupture in the tank. Failure to comply is a fine in six figures.
Trade: Excavation
Thanks for the feedback. Rex, it either is or is close to 3/8. What psi should I bring those up to for a safe check?
Will do on checking with environ authorities. |
The Grand Wazoo
Here I think they test tanks at 40 PSI, but don't quote me on that, fuel tanks are their own business here because of all the EPA regulations.
Read here, you have to be certified to do this work.
http://maine.gov/dep/rwm/ust/index.htm Why does he want this dug up? Someone should test the tank and lines first to see if digging it up is even necessary. As for testing the lines, do you have a nitrogen test setup. From the website link above: Precision Testing Requirements According to Chapter 691 a “Precision Test” means a tank and piping line tightness test, approved by the commissioner, that is capable of detecting a leak, a loss or gain of 0.1 gallon per hour with a probability of detection of at least 95 percent and a probability of a false alarm of five (5) or less percent as determined by an by an independent testing laboratory in accordance with U.S. Environmental Protection Agency approved protocols, or other protocols approved by a nationally recognized independent testing organization, including but not limited to the ASTM and the National Work Group on Leak Detection Evaluations. (Chapter 691, Section 3(LL)) Piping Line Tightness Test Requirements All pressurized product piping tests must be preformed at 150% operating pressure, or if performed at a lower pressure, it must be able to obtain a leak rate equivalent or smaller than that determined by the piping test method’s independent performance testing in accordance with U.S. Environmental Protection Agency approved protocols. (Chapter 691, Appendix B(3)(A)) All tests must be preformed in strict conformity to all of the testing equipment manufacturer’s standard operating procedures. In addition, the test must be run a minimum of one hour. (Chapter 691, Appendix B(3)(B)) Additional Requirements All testing technicians shall be certified by the manufacturer of the testing equipment. (Chapter 691, Appendix B(4)(A)) All test results must include the following information in order to be accepted by the commissioner: (1) Facility name, address, registration and tank number, and the product stored; (2) Whether the facility components tested passed or failed, and the measured leak rate; (3) The test method’s threshold for declaring a leak; and (4) Certification that the test method has been performed according to the manufacturer’s protocols used in the third party evaluation. (Chapter 691, Appendix B(4)(B)) Reminder According to Chapter 691, all tests must be preformed in strict conformity to all of the testing equipment manufacturer’s standard operating procedures and with any limitations determined by an independent testing laboratory in accordance with U.S. Environmental Protection Agency approved protocols, or other protocols approved by a nationally recognized independent testing organization, including but not limited to the ASTM and the National Work Group on Leak Detection Evaluations. (Chapter 691, Section 3(LL) and Chapter 691, Appendix B(1)(D)) Last edited by Kgmz; 03-26-2008 at 10:36 PM. |
#7 | |
Professional
Trade: General Contractor Commercial Facility Maintenance Services
Re: Underground Diesel TankQuote:
| Diesel Generator - home backup | Syborg_97 | Electrical | 11 | 03-07-2008 07:39 PM |
| Heating Oil Tank Venting | RenaissanceR | HVAC | 1 | 01-02-2008 07:41 PM |
| Wiring/grounding for diesel tank? | jimb317 | Electrical | 3 | 10-20-2007 05:58 PM |
| septic tank replacement | loogout1 | Excavation & Site Work | 14 | 10-05-2007 08:23 AM |
| Consolidated Diesel Electric Genset | thecrose12 | Electrical | 0 | 03-08-2004 04:34 PM |