Trade: LANDSCAPER
Gas Drier Venting
What is acceptable plumbing codes-wise regarding venting my gas drier to my crawl space instead of to the outdoors? Is a special box to filter things out necessary?
Trade: Squirrel Handler
Re: Gas Drier Venting
There is actually an indoor dryer vent kit but I would never use one nor would I vent it in the crawl space. The lint is a fire hazard and the moisture can cause all types of problem like mold, mildew and wood rot. Get an electric dryer if you don't want a vent.
I forgot about the code question, every place I know of it's against code. Last edited by mickeyco; 03-05-2007 at 10:24 PM. |
Plumber
Trade: Plumbing
There is no way to filter out carbon monoxide. Bad stuff...Seems to me that electric dyers also utilize a vent. For lint, heat, and moisture. You should vent it to outside. The lint alone makes for an extremely dangerous situation. I have been under houses where I refused to fire up my torch.
Worried what could ignite! You need to get that stuff to the outside Last edited by gmp; 03-05-2007 at 11:12 PM. |
The electric dryers do have a vent but for electric you can use the indoor vent that has a lint trap.
http://doitbest.com/DoItBest/Main.as...associate=true |
#5 | |
Re: Gas Drier VentingQuote:
Problems aside, it is technically a code violation.
CLOTHES DRYERS EXHAUST M1501.1 General. Dryer exhaust systems shall be independent of all other systems, shall convey the moisture to the outdoors and shall terminate on the outside of the building. Exhaust duct terminations shall be in accordance with the dryer manufacturer's installation instructions. Screens shall not be installed at the duct termination. Exhaust ducts shall not be connected with sheet-metal screws or fastening means which extend into the duct. Exhaust ducts shall be equipped with a backdraft damper. Exhaust ducts shall be constructed of minimum 0.016-inch-thick (0.406 mm) rigid metal ducts, having smooth interior surfaces with joints running in the direction of air flow. Flexible transition ducts used to connect the dryer to the exhaust duct system shall be limited to single lengths, not to exceed 8 feet (2438 mm) in length and shall be listed and labeled in accordance with UL 2158A. Transition ducts shall not be concealed within construction. Exception: This section shall not apply to listed and labeled condensing (ductless) clothes dryers. |