I am a carpenter by trade but have decided to build my own garage here in Ottawa. I will be using a 4" concrete slab on grade with 6" wide by 12" high perimeter wall to keep wood walls away from the ground. After digging down 2' of pure sand, I decided to stop, compact it and fill the hole with gravel. I plan on reinforcing the slab with 15M bars on 12" centers both ways and put two around the slab perimeter and one inside the perimeter wall. I will be building 10' high walls with 2X6 then put on the roof. There will be a 16' X 8' garage door for entry. I have never done any work with rebar or concrete before so don't know if this plan will be adequate? Should I thicken the slab around the edge or maybe the whole thing? Should I use more reinforcement or use it differently? It gets very cold here in winter (-30C) and hot in summer (+30C), should I use any expansion joints? Should I take special care at the opening of the garage?

The old garage was built around 1913 directly on the ground and held up until now. There was no bottom plate left and the stud ends were rotten. the whole thing sank at least 6 inches. I can't believe it lasted 100 years. I want the new garage to last even longer. Probably going to use pressure treated for bottom plate. The concrete is what worries me in this situation, don't want it to crack or crumble too quickly.
HHC is offline  

Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

   
 

Old 03-27-2010, 10:17 PM   #2
SEMI RETIRED
 
griz's Avatar
 
Trade: General Contractor
Join Date: Nov 2009
Location: CA
Posts: 13,615
Rewards Points: 4,392

Re: Garage Slab 20' X 20' Edge Concerns


Your local code will dictate how the footing should be done.
I like the idea of the footing to elevate the wall. Your rebar idea sounds a bit over kill. If your in rain country provide a depression in the slab where your door closes, about an inch deep, 6" wide and about 3" wider than your door opening to keep water out. Yes, use expansion joints. I'd also provide a 3'man door for entry.

griz is online now  
Old 03-28-2010, 12:52 AM   #3
Pro
 
mics_54's Avatar
 
Trade: contractor
Join Date: Oct 2008
Posts: 1,067
Rewards Points: 500

Re: Garage Slab 20' X 20' Edge Concerns


You can build a frost protected slab on grade if the building is heated.

http://www.nahb.org/assets/docs/publ...00244041PM.pdf

Last edited by mics_54; 03-28-2010 at 01:03 AM.
mics_54 is offline  
Old 03-28-2010, 01:17 AM   #4
Pro
 
CanCritter's Avatar
 
Trade: bricklayer/stonemason
Join Date: Feb 2010
Location: Calgary
Posts: 310
Rewards Points: 312

Re: Garage Slab 20' X 20' Edge Concerns


dont belive it would pass code up here
CanCritter is offline  
Old 03-28-2010, 09:25 AM   #5
Sure, I can do that...
 
jlhaslip's Avatar
 
Trade: carpentry/renovations
Join Date: Dec 2009
Location: Golden, BC, Canada
Posts: 539
Rewards Points: 500
Send a message via Skype™ to jlhaslip

Re: Garage Slab 20' X 20' Edge Concerns


thickened edge slab detail for Canadian climate
Attached Thumbnails
Garage slab 20' X 20' edge concerns-screenshot-deltacad-thick_slab.dc-.png  
jlhaslip is offline  
Old 03-28-2010, 10:30 AM   #6
Pro
 
mics_54's Avatar
 
Trade: contractor
Join Date: Oct 2008
Posts: 1,067
Rewards Points: 500

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CanCritter View Post
dont belive it would pass code up here
#1) I wouldn't have suggested it had I thought it wouldn't.

#2) More than one million FPSFs have been built over the past
45 years in Norway, Sweden and Finland, where they have
been approved by code since the 1970s. In Scandinavia, the
method is standard practice for low-rise construction,
including homes, townhouses, shopping malls, stores, office
buildings and schools. In the lower U.S., an estimated 3,000
FPSFs had been built by 2000, including single family
houses, townhouses, housing for the elderly and disabled,
additions, apartments, stores, and other commercial
buildings.
Additional FPSFs have been built in Alaska and Canada.
The U.S. Army has built several FPSFs, including an
addition to a conventional deep foundation for an airport
control tower in Galena, Alaska, near the Arctic Circle,
where the frost depth is 13 feet and winter temperatures
reach -60 F for weeks at a time. No frost heave or differential
settlement has been observed. For more information
see www.geofoam.org/pdfs/CRREL9707.pdf.
mics_54 is offline  
Old 03-28-2010, 11:01 AM   #7
New Guy
 
HHC's Avatar
 
Trade: Framing contractor
Join Date: Feb 2010
Location: Ottawa
Posts: 25
Rewards Points: 10

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by griz View Post
Your local code will dictate how the footing should be done.
I like the idea of the footing to elevate the wall. Your rebar idea sounds a bit over kill. If your in rain country provide a depression in the slab where your door closes, about an inch deep, 6" wide and about 3" wider than your door opening to keep water out. Yes, use expansion joints. I'd also provide a 3'man door for entry.
Yes, I forgot to say, there is a 3' man door at the left rear and window somewhere on the left side. I don't believe in overkill, only underkill. Rebar is already ordered so it is too late anyway. It will be here tomorrow. I like your idea for the depression at the door, will definitely do that. What spacing should be used for the expansion joints? Should they be in the floor and ledge? I have included pictures taken today to show what I am talking about. I will finish the ledge formwork around the right side today. We will be placing the rebar tomorrow.
Attached Thumbnails
Garage slab 20' X 20' edge concerns-img_1754a.jpg   Garage slab 20' X 20' edge concerns-img_1755a.jpg  
HHC is offline  
Old 03-28-2010, 11:05 AM   #8
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by HHC View Post
I am a carpenter by trade but have decided to build my own garage here in Ottawa. I will be using a 4" concrete slab on grade with 6" wide by 12" high perimeter wall to keep wood walls away from the ground. After digging down 2' of pure sand, I decided to stop, compact it and fill the hole with gravel. I plan on reinforcing the slab with 15M bars on 12" centers both ways and put two around the slab perimeter and one inside the perimeter wall. I will be building 10' high walls with 2X6 then put on the roof. There will be a 16' X 8' garage door for entry. I have never done any work with rebar or concrete before so don't know if this plan will be adequate? Should I thicken the slab around the edge or maybe the whole thing? Should I use more reinforcement or use it differently? It gets very cold here in winter (-30C) and hot in summer (+30C), should I use any expansion joints? Should I take special care at the opening of the garage?

The old garage was built around 1913 directly on the ground and held up until now. There was no bottom plate left and the stud ends were rotten. the whole thing sank at least 6 inches. I can't believe it lasted 100 years. I want the new garage to last even longer. Probably going to use pressure treated for bottom plate. The concrete is what worries me in this situation, don't want it to crack or crumble too quickly.
Sounds good, 12"high curb maybee a little high, 8" above grade is a good alternative. I would pour a footing 36"depth or a 16"depth thicken edge, you can also run your rebar into footing and slab and pour it monolithic. A 4" concrete slab is good, 6 1/2 sac with 6% air, no10 wwm, and a fiber is good for a secondary reinforcement. I would not pour anything thicker, unless you plan on exceeding 4500psi. No need for expansion joint in slab.

Last edited by CONCRETE MIKE; 03-28-2010 at 11:56 AM.
CONCRETE MIKE is offline  
Old 03-28-2010, 11:10 AM   #9
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by HHC View Post
Yes, I forgot to say, there is a 3' man door at the left rear and window somewhere on the left side. I don't believe in overkill, only underkill. Rebar is already ordered so it is too late anyway. It will be here tomorrow. I like your idea for the depression at the door, will definitely do that. What spacing should be used for the expansion joints? Should they be in the floor and ledge? I have included pictures taken today to show what I am talking about. I will finish the ledge formwork around the right side today. We will be placing the rebar tomorrow.
Not a bad set up, i would dig futher down below grade for a thickened edge. Are you going with a 12" over hang on front of garage? And are you going to have a 1" lip at front of the slab? I would also brace your outside walls better, i see that you are using 1" x 12" plywood for your outside forms, they might bow. Run your strong back and kickers every 2', it is better to over kick than under kick. I looked again at your set up, you need to run a strong back and kick at bottom and top, or your form work will bow and blow out. And for your inside curb forms i would also run some 3' steel pins to prevent bowing also. Well i see that you ran wall ties at the bottom, or are they spreaders?

Last edited by CONCRETE MIKE; 03-28-2010 at 11:31 AM.
CONCRETE MIKE is offline  
Old 03-28-2010, 11:40 AM   #10
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Here in cleveland ohio we also have alot of sand near lake erie and very bad winters, our local codes require a 36" footing on slabs 400sf or more. That is going to be a pain in the ass to strip and rub the inside walls, are you pouring the walls and floor monolithic? Remember most of your pressure will be at the bottom of your wall, brace bottom! Pour walls stiff and vibrate.

Last edited by CONCRETE MIKE; 03-28-2010 at 11:55 AM.
CONCRETE MIKE is offline  
Old 03-28-2010, 11:54 AM   #11
New Guy
 
HHC's Avatar
 
Trade: Framing contractor
Join Date: Feb 2010
Location: Ottawa
Posts: 25
Rewards Points: 10

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CONCRETE MIKE View Post
Not a bad set up, i would dig futher down below grade for a thickened edge. Are you going with a 12" over hang on front of garage? And are you going to have a 1" lip at front of the slab? I would also brace your outside walls better, i see that you are using 1" x 12" plywood for your outside forms, they might bow. Run your strong back and kickers every 2', it is better to over kick than under kick. I looked again at your set up, you need to run a strong back and kick at bottom and top, or your form work will bow and blow out. And for your inside curb forms i would also run some 3' steel pins to prevent bowing also. Well i see that you ran wall ties at the bottom, or are they spreaders?
Digging at the edge will not be a problem, there is 30 tons of stone in this hole, 2 feet deep in some places. I will definitely do that today. I will have a gable roof, 4/12 pitch to not exceed height restriction, 2' overhang at front and 1' overhang at sides and rear. There is at least a 1" lip at front of the slab. The new driveway will be paved to meet in on a 1-2% incline. All formwork is 3/4" plywood. The outside forms are actually 3' wide, 2' below ground to the sand. We placed those before the gravel. The bottom of the outside form can't go anywhere as it is filled on both sides below grade. The top edge of the outside form is not fully braced yet. It may not show well in the picture but I screwed 6" steel ties at 3' spacing 1" above bottom of inside form to the outside form to prevent bottom of inside form kicking out. The top spreaders are spaced every 4'. All forms are screwed together with 1.5" screws. I will probably add a few 2" screws before pouring the concrete. Thanks for the advice. I must get out there and work!
HHC is offline  
Old 03-28-2010, 11:55 AM   #12
New Guy
 
HHC's Avatar
 
Trade: Framing contractor
Join Date: Feb 2010
Location: Ottawa
Posts: 25
Rewards Points: 10

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by jlhaslip View Post
thickened edge slab detail for Canadian climate
Thanks for the detail! It makes sense. What do the blue lines represent? I assume the dots are rebar.
HHC is offline  
Old 03-28-2010, 12:04 PM   #13
New Guy
 
HHC's Avatar
 
Trade: Framing contractor
Join Date: Feb 2010
Location: Ottawa
Posts: 25
Rewards Points: 10

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CONCRETE MIKE View Post
Here in cleveland ohio we also have alot of sand near lake erie and very bad winters, our local codes require a 36" footing on slabs 400sf or more. That is going to be a pain in the ass to strip and rub the inside walls, are you pouring the walls and floor monolithic? Remember most of your pressure will be at the bottom of your wall, brace bottom! Pour walls stiff and vibrate.
I was planning on pouring all at the same time , monolithic, but don't have the confidence to do it without an expert. I want to have it all set up properly then bring in a finisher to help on pour day. Was planning on renting a vibrator for sure.
HHC is offline  
Old 03-28-2010, 12:05 PM   #14
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by HHC View Post
Digging at the edge will not be a problem, there is 30 tons of stone in this hole, 2 feet deep in some places. I will definitely do that today. I will have a gable roof, 4/12 pitch to not exceed height restriction, 2' overhang at front and 1' overhang at sides and rear. There is at least a 1" lip at front of the slab. The new driveway will be paved to meet in on a 1-2% incline. All formwork is 3/4" plywood. The outside forms are actually 3' wide, 2' below ground to the sand. We placed those before the gravel. The bottom of the outside form can't go anywhere as it is filled on both sides below grade. The top edge of the outside form is not fully braced yet. It may not show well in the picture but I screwed 6" steel ties at 3' spacing 1" above bottom of inside form to the outside form to prevent bottom of inside form kicking out. The top spreaders are spaced every 4'. All forms are screwed together with 1.5" screws. I will probably add a few 2" screws before pouring the concrete. Thanks for the advice. I must get out there and work!
I see. Good luck, put expansion at front of garage where drive will meet garage slab.
CONCRETE MIKE is offline  
Old 03-28-2010, 12:09 PM   #15
Pro
 
CanCritter's Avatar
 
Trade: bricklayer/stonemason
Join Date: Feb 2010
Location: Calgary
Posts: 310
Rewards Points: 312

Re: Garage Slab 20' X 20' Edge Concerns


this is canada..not alaska sweden or germany so those codes arent prevalant here...l was just looking into building a garage a mnth ago in manitoba..they said no go for slab foundations...my foundation would have to be below the frost line to pass code....personaly ld sooner go with a slab as its cheaper and easyer but alas codes say no in Manitoba or l was missinformed...in anycase the codes across canada are pretty much standard so will have to look into it more and have sent inquireies to both Manitoba and Ottawa for clarification....do you have a building permit for slab on grade desighn?
CanCritter is offline  
Old 03-28-2010, 12:18 PM   #16
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CanCritter View Post
this is canada..not alaska sweden or germany so those codes arent prevalant here...l was just looking into building a garage a mnth ago in manitoba..they said no go for slab foundations...my foundation would have to be below the frost line to pass code....personaly ld sooner go with a slab as its cheaper and easyer but alas codes say no in Manitoba or l was missinformed...in anycase the codes across canada are pretty much standard so will have to look into it more and have sent inquireies to both Manitoba and Ottawa for clarification....do you have a building permit for slab on grade desighn?
So you live on mars?
CONCRETE MIKE is offline  
Old 03-28-2010, 01:23 PM   #17
Pro
 
CanCritter's Avatar
 
Trade: bricklayer/stonemason
Join Date: Feb 2010
Location: Calgary
Posts: 310
Rewards Points: 312

Re: Garage Slab 20' X 20' Edge Concerns


if you have something inteligent to say please do...baiting me aint gona git you nowhere son
CanCritter is offline  
Old 03-28-2010, 01:46 PM   #18
Sure, I can do that...
 
jlhaslip's Avatar
 
Trade: carpentry/renovations
Join Date: Dec 2009
Location: Golden, BC, Canada
Posts: 539
Rewards Points: 500
Send a message via Skype™ to jlhaslip

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by HHC View Post
Thanks for the detail! It makes sense. What do the blue lines represent? I assume the dots are rebar.
the blue lines are re-bar running across the slab/footer.

used this design on my own shop/garage 5 years ago. a few hairline cracks popped up the first winter, but have not gotten any worse in 5 years.
Area it was built does not required a building permit, but I have done the same design in town several times under permit. no issues.

Last edited by jlhaslip; 03-28-2010 at 01:50 PM.
jlhaslip is offline  
The Following User Says Thank You to jlhaslip For This Useful Post:
HHC (03-29-2010)
Old 03-28-2010, 02:53 PM   #19
Concrete Mike
 
CONCRETE MIKE's Avatar
 
Trade: concrete
Join Date: Jan 2010
Location: ohio
Posts: 285
Rewards Points: 250

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CanCritter View Post
if you have something inteligent to say please do...baiting me aint gona git you nowhere son
If I was baiting you I would have used a zara spook or a hj12 huskey jerk, with 10 lb spider wire!
CONCRETE MIKE is offline  
Old 03-28-2010, 04:13 PM   #20
New Guy
 
HHC's Avatar
 
Trade: Framing contractor
Join Date: Feb 2010
Location: Ottawa
Posts: 25
Rewards Points: 10

Re: Garage Slab 20' X 20' Edge Concerns


Quote:
Originally Posted by CanCritter View Post
this is canada..not alaska sweden or germany so those codes arent prevalant here...l was just looking into building a garage a mnth ago in manitoba..they said no go for slab foundations...my foundation would have to be below the frost line to pass code....personaly ld sooner go with a slab as its cheaper and easyer but alas codes say no in Manitoba or l was missinformed...in anycase the codes across canada are pretty much standard so will have to look into it more and have sent inquireies to both Manitoba and Ottawa for clarification....do you have a building permit for slab on grade desighn?
You are allowed to use slab on grade design for accessory structures up to 592 square feet. This applies to all of Ontario, I don't know about other provinces. I am waiting on truss drawings and will be issued permit when they are submitted. Check out: http://www.cambridge.ca/relatedDocs/...ril%202009.pdf
This is the best site I have found for garage requirements.

Here are some updated pictures of my garage. I haven't done the digging around the perimeter to give it the shape in the drawing posted a few above. That will be tomorrow's work.
Attached Thumbnails
Garage slab 20' X 20' edge concerns-img_1756a.jpg   Garage slab 20' X 20' edge concerns-img_1758a.jpg  

HHC is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deep fill under garage slab lazerguy Masonry 25 08-06-2014 08:37 AM
Concrete overlay over existing garage slab daft_GC Concrete & Paving 10 11-19-2009 07:42 AM
Price for Fill / Garage Slab Prep -- Opinions? slr2974 Excavation & Site Work 9 06-17-2009 09:22 AM
Pin your garage slab into the stemwalls? Halo Concrete & Paving 5 03-11-2009 10:53 AM
Garage Floor Slab WNYcarpenter Masonry 3 11-17-2008 12:16 PM

Join Now... It's Fast and FREE!

I am a professional contractor
I am a DIY Homeowner
Drywall Talk is for
PROFESSIONAL CONTRACTORS ONLY!

At DrywallTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?