Underground In Building Low Voltage
Old 03-20-2009, 08:30 AM   #1
OhioTelecom's Avatar
Trade: Telecommunications
I was told by an inspector that my low voltage cable even though the conduits are all within the building would require underground rated cable. He let me slide this time...
I understand if we were leaving the building, but there is no way for water, from outside to go under the walls, move X amount of feet into the store, then up into a conduit.
Example:
There are several conduits originating in the electrical room, then go under ground to various locations within the building never leaving the building at all.
OhioTelecom is offline
Old 03-22-2009, 07:32 AM   #2
Baltimore Electrician
JohnJ0906's Avatar
Trade: Electrician
Re: Underground In Building Low Voltage
Example:
See 300.5(B). Underground is not inside the building.
HOWEVER, that may not apply to your installation. Exactly what are you installing? If it is a chapter 8 install, 300.5 might not apply.
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline
Old 03-22-2009, 01:21 PM   #3
Sorry, it is all Cat 5e cable PVC.
Old 03-22-2009, 02:27 PM   #4
JohnJ0906's Avatar
Trade: Electrician
I would think wet rated cable is what should be used. It isn't direct buried
No conduit is 100% watertight. That is why "W" rated cables and conductors are required. Over time, condensation alone will cause moisture in the conduit
Example:
If it is a grade level slab, you are not inside the building. That is a wet location.
However, if this is a Article 800 installation, I see nothing that would actually require a "w" rated cable, although it would be a very good idea, in my opinion.
John from Baltimore
"One Day at a Time"
Old 03-22-2009, 03:22 PM   #5
mdshunk's Avatar
I agree.... using flooded cable is a good idea in underground cable installs, but there's not a thing in Chapter 8 that would require you to do so. The mere existence of such a product does not necessitate its installation. Ask the inspector for a code citation next time.
mdshunk is offline
Joasis (and others) how much would this building cost in your area? Mike Finley Construction 8 09-15-2008 03:51 PM
??? Whats the best way to spread the news about your company? jmgrahamjr Marketing & Sales 21 06-24-2008 04:46 AM
Certified Green Building Professional Training CatAlii Green Building 6 05-11-2008 04:20 PM
Nobody Wants to bid Deutsche Bank Building Now Wolf Demolition 2 08-26-2007 03:37 PM
Conduit for underground low voltage wire robertc65 Outdoor Lighting 4 01-22-2007 02:52 PM