Parking Lot Lights Questions
Old 06-20-2008, 12:13 PM   #1
Midwestguy954's Avatar
Trade: Electrician
I'm going to wire 6 parking lots lights on poles that have been put up already and I have a couple questions. The lights are 120vac MH, poles are metal, bolted to new concrete pads. The installers have 2inch PVC underground from pole to pole, and are ready for me to pull in the wire. Do I need to sink in a ground rod at each pole, or is a properly sized ground wire back to the dist. panel in main building all that is needed? Is surge suppression required or a good idea? And if so would you recommend one at each pole or just at the dist. panel in main building. Is GFI protection required? Any other precautions that you can think of I would appreciate knowing. Thank You.
Midwestguy954 is offline
Old 06-20-2008, 03:25 PM   #2
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
Re: Parking Lot Lights Questions
I don't know. What does 210.8(B) say?
Speedy Petey is offline
Old 06-20-2008, 05:23 PM   #3
Service & Repairs
Magnettica's Avatar
Trade: Electrician
I think a properly sized equipment grounding conductor (EGC) is all that he needs, but I would check with what the manufacturer of the light specs-out. My biggest concern for the parking lot lights would be voltage drop. Remember to size your EGC based on the size of your overcurrent protection, not the size of the wires going to each pole. No GFCI protection for me, thanx.
Magnettica is offline
Old 06-21-2008, 06:56 AM   #4
Baltimore Electrician
JohnJ0906's Avatar
Trade: Electrician
Don't forget 250.122(B)
If the circuit conductors are increased for voltage drop, the EGC must be increased.
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline
Old 06-21-2008, 07:47 AM   #5
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Thanks John.
Old 06-21-2008, 07:48 AM   #6
JohnJ0906's Avatar
Trade: Electrician
Originally Posted by Magnettica View Post
Thanks John.
You're welcome.
John from Baltimore
"One Day at a Time"
Old 06-21-2008, 09:29 AM   #7
Trade: Electrician
Thanks for all your replies.
Old 07-19-2008, 04:27 PM   #8
Master Electrician
Bubbles's Avatar
Trade: Electrical
Just wondering the "why" of 250.122. Do you happen to know? EX. 4/0 200 amp service with only #6 to ground rod and #4 to water pipe. Good or bad analogy? Curious as to if the lights are on a 2pole 20 amp breaker and have #4's or #6's ran out to lights...why identical ground? It used to be 2 sizes below just a few years ago if I recall??
your friend
Bubbles is offline
Old 07-19-2008, 10:02 PM   #9
JohnJ0906's Avatar
Trade: Electrician
your friend
Think about this for a minute.
Why increase the wire size? Voltage drop.
What causes voltage drop? The resistance of the wire itself.
To reduce that resistance, and the voltage drop, increase the wire size.
Therefore, we might have #8 or #6 on a 20 amp circuit.
OK, now, why increase the EGC size?
What is the EGC for? Low impedance fault path. In a long circuit, the conductor resistance will affect the OCPD operation. Less amperage, longer to trip - or it might not trip at all.
The same reasons for increasing conductor size for the circuit conductors apply to the EGC as well.
John from Baltimore
"One Day at a Time"
Old 07-19-2008, 10:04 PM   #10
JohnJ0906's Avatar
Trade: Electrician
your friend
Oh, and this is a very bad analogy. The Equipment Grounding Conductor and the Grounding Electrode Conductor are 2 different creatures - the GEC, and connecting to the planet Earth, has nothing to do with the operation of an OCPD at the <600 volt level.
John from Baltimore
"One Day at a Time"
Old 07-19-2008, 11:20 PM   #11
Master Electrician
Bubbles's Avatar
Trade: Electrical
Makes sense to me.
thanks
Bubbles is offline
Wiring shop lights. ryan.s Electrical 14 04-10-2008 11:17 PM
Pricing questions Brian Painting & Finish Work 3 10-13-2007 09:38 AM
Installation Of recessed lights Morry Electrical Picture Post 20 07-20-2007 09:56 PM
Digging Under The Lights? denick Excavation & Site Work 9 02-28-2007 06:52 AM