Trade: General
Kitchen Counter Recepticle
Inspector refused our final today. He said, we did not meet NEC regarding the spacing and number of recepticles at the kitchen counter.
I am sure this will be a quick answer, but how often are you required to have recepticles at a kitchen counter and what section of NEC is this mentioned? The inspector said we are required to have a recepticle ever 24". Also does anyone know what year of NEC Texas requires? Thanks. |
Service & Repairs
Trade: Electrician
Re: Kitchen Counter Recepticle
Do you have your own copy of the NEC? If yes, then look at article 210.52. There's a whole lot there but it really isn't that difficult.
In a nutshell, a receptacle is required on a kitchen countertop wherever the counterspace is larger than 12", and no more than 48" apart from one receptacle to the other. All of them have to be GFCI protected. This includes all countertops in the kitchen. |
| The Following User Says Thank You to Magnettica For This Useful Post: | DallDev (04-30-2009) |
Trade: General
Thanks.
I don't have a copy of NEC. The kitchen has GFCI recpticle within 42" of each other; however, the inspector says I am required to have a recepticle every 24". That sounds to often? |
#4 | ||
And I do electrical, too!
Re: Kitchen Counter RecepticleQuote:
You need to get one.
Site : the area or exact plot of ground on which anything is, has been, or is to be located. Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision. Cite : To mention in support, proof, or confirmation; refer to as an example. Last edited by 480sparky; 04-30-2009 at 11:21 PM. |
| The Following User Says Thank You to 480sparky For This Useful Post: | DallDev (04-30-2009) |
#5 | |
Doofenshmirtz Evil Inc.
NEC 210.52 At kitchen countertops, receptacle outlets shall be installed so that no point along the wall line is more than 24 inches measured horizontally from a receptacle. edit...you beat me to it 480.
in texas with framing and cornish people will do it for 3.00 a foot. What do yall think about that? Just laber |
| The Following User Says Thank You to JumboJack For This Useful Post: | DallDev (04-30-2009) |
Trade: General
Actually in addition the inspector is requiring me to have recepticles for the islands the main island has a veg sink and is 7 foot long. He has stated that he wants me to put a wire mold type strip at least 4 foot long underneath the counter top.
The main island sink and counter top has a left hand wing of 64 inches long with a dishwasher to the left of the sink. The electrician installed a plug on the end of the counter and now the inspector wants another plug on either side of the dish washer and on the right side of the sink he wants a second plug in addition to the end counter plug two foot from the end right next to the sink area. This side of the counter is 48 inches long. |
#7 | |
This stuff should have been caught on rough inspection.Your sparky should have known this but it is you,the GC,that needs to know this stuff...
#1 stunner
Island 210.52 c2
You need to get a code book.
Trade: General
Will be getting a code book tomorrow but wanted some help to narrow down the reading. We have plugs in the end of the island on both sides. What the inspector is requesting is a plug every 24 inches in the island not a measured 24 inches from the plugs.
Rough in inspections never have cabinets installed, that would be premature. The island had underground electricial but the owners changed a few items with the cabinet man. Both islands have GFI plugs installed at the ends of the islands. |
Service & Repairs
Trade: Electrician
Buying the code book is a step in the right direction but you may also want to consider buying an illustrated guide to the code because if you've never read the NEC before you have a headache in your future. The good news is you have sites like this (and some others) where we are more than happy to answer any questions.
#11 | |
#1 stunner
At least one receptacle shall be installed at each island counter space with a long dimension of 24" or greater and a short dimension of 12" or greater. Where a rangetop or sink is installed in an island counter and the width of the counter behind the range top or sink is less that 12", the rangetop or sink is considered to divide the island into two separate counter top spaces as defined in 210.52c4 |
#12 | |
the way you have to do it.
DallDev.... get two Codebooks, one for you and one for your inspector.
Your inspector is a
Site : the area or exact plot of ground on which anything is, has been, or is to be located. Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision. Cite : To mention in support, proof, or confirmation; refer to as an example. |
woodchuck2
http://www.neca-neis.org/state/state_regs.cfm This will tell you what is required in Texas.
#1 stunner
Re: Kitchen Counter Recepticle |
#16 | |
Trade: Electrical
![]() Who's with me?
#17 | |
Trade: Electrical
#18 |
I'm willing to bet this inspector isn't just an electrical inspector, but more likely a multi-trade inspector....... footings, framing, mechanical, plumbing, electrical, etc. Jack of all trades and master of none.
#19 | |
Trade: Design
#20 |
Trade: Electrical
Where are you in Tx Dall?
| Tags |
i am sleepy ![]() |
| Google Seminars For Success... | Ivinni | Marketing & Sales | 193 | 02-07-2009 08:22 PM |
| New Kitchen Counter | genecarp | Concrete & Paving | 0 | 11-07-2008 05:26 PM |
| granite tiles on kitchen counter | lornmastro | Flooring | 13 | 02-24-2008 05:32 PM |
| Looking to change kitchen counter top | gofrugal | Remodeling | 28 | 02-08-2008 10:50 PM |
| kitchen counter tops | i_plant_art | Remodeling | 9 | 01-26-2006 07:23 PM |