A Couple NEC Questions
Old 04-30-2009, 06:43 PM   #1
NightLightingFX's Avatar
Trade: Artistic Outdoor Lighting
As a low voltage landscape lighting professional I rarely need permits so I don't know the NEC very well. I have 2 questions I would appreciate you guys helping me out on:
1) Can you have more than 3 currents carrying conductors in a raceway without derating them the 80%?
2) What is the max lenght of conduit you can run without de-rating?
Thanks
~Ned
Ned Hastings CLVLT #0852
Night Lighting FX
www.nightlightingfx.com
NightLightingFX is offline
Old 04-30-2009, 06:55 PM   #2
And I do electrical, too!
480sparky's Avatar
Re: A Couple NEC Questions
Originally Posted by NightLightingFX View Post
.......1) Can you have more than 3 currents carrying conductors in a raceway without derating them the 80%?
If you meet any of the exceptions to 310.15(C)(2)(a), you can.
2) .......What is the max lenght of conduit you can run without de-rating?.........
There is no maximum length when it comes to derating. Raceway length is only limited by how long you can get conductors, and your method to pull them in.
Site : the area or exact plot of ground on which anything is, has been, or is to be located.
Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision.
Cite : To mention in support, proof, or confirmation; refer to as an example.
480sparky is offline
Old 04-30-2009, 08:48 PM   #3
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
What type and size of conductors?
If you are working with #14, #12 or #10 then you should not have to worry about derating until you reach NINE CCC's.
Remember, the neutral of a MWBC is not counted as a CCC with regard to derating.
I am curious. What do permits have to do with knowing the codes related to your trade?
Speedy Petey is offline
Old 04-30-2009, 10:14 PM   #4
Service & Repairs
Magnettica's Avatar
Trade: Electrician
480, I think what the OP was asking about as far as the maximum size length conduit before needing to derate would be 24".
Magnettica is offline
Old 04-30-2009, 10:24 PM   #5
480sparky's Avatar
I think you're right about the nipple length, but that would be 600 mm, not 24 inches.
Old 04-30-2009, 10:45 PM   #6
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Oh, lol. Is that what 310.15(C)(2)(a) says? I don't have my book in front of me and I'm in the middle of filing some crap with the my new business partner the IRS.
Old 04-30-2009, 11:17 PM   #7
480sparky's Avatar
No, that comes from Chapter 9, Note 4.
Old 05-01-2009, 11:07 AM   #8
Thanks for the response guys I appreciate it.
~Ned
Night Lighting FX
Old 05-01-2009, 01:22 PM   #9
ampman
ampman's Avatar
Trade: providing pathways for electrons and protons
i thought the 24" nipple rule was for conduit fill not conductor derating
ampman is offline
Old 05-01-2009, 03:16 PM   #10
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Good question.
310.15(B)(2)(a) Exception No. 3: Derating factors shall not apply to con-
ductors in nipples having a length not exceeding 600 mm
(24 in.).
Old 05-01-2009, 04:23 PM   #11
480sparky's Avatar
Good question.
(24 in.).
As well as Ch. 9, Note 4:
(4) Where conduit or tubing nipples having a maximum length not to exceed 600 mm (24 in.) are installed between boxes, cabinets, and similar enclosures, the nipples shall be permitted to be filled to 60 percent of their total cross-sectional area, and 310.15(B)(2)(a) adjustment factors need not apply to this condition.
Old 05-01-2009, 10:00 PM   #12
ampman
ampman's Avatar
so its settled no derating of conductors in conduit 24"(600 mm) or less and fill @ 60 % for two conductors and over
ampman is offline
Old 05-01-2009, 10:02 PM   #13
480sparky's Avatar
I second that.
Old 05-01-2009, 10:02 PM   #14
ampman
ampman's Avatar
they are a silent partner unless dont pay
ampman is offline
Marketing Questions chezziepoo Marketing & Sales 10 01-27-2009 10:52 AM
couple questions atticstobasemen Marketing & Sales 6 12-31-2008 09:02 AM
2 questions, arc fault & light feed Burby Electrical 13 12-23-2008 05:50 PM
Cork Flooring Questions.... SBI Flooring 3 12-12-2008 04:18 PM
Couple of questions about expansion joints. ruskent Masonry 3 08-20-2007 03:53 PM