Trade: Commercial/Residental Construction
Breaker/Conductor Size On HVAC Equipment
I'm wiring a heat pump compressor.
Specs- 19 min circuit ampacity, 25 min, 30 max breaker sizes. All right off of the nameplate. Using 12 ga. NM cable(existing in this case), I must use the 60C column of 310.16. Which allows 25 amps. So can I use a 25 amp breaker on #12? By referring to 240.4(D) which sends me to 240.4(G) then to Art 400 Parts III and VI Here's where I get confused. I cannot find where the code states that I can use the 25 ampacity figure instead of the 20 for #12 NM cited by 240.4D. What I'm I missing? |
#2 | |
Baltimore Electrician
Trade: Electrician
Re: Breaker/Conductor Size On HVAC Equipment
Section 440 Air Conditioning and Refrigerating Equipment - specificaly parts III and IV - it doesnt come right out and say "you can do this " but it tells you to calculate conductors at 125% and short circuit protection at 175%. The only thing you need to see is "min circuit ampacity"-19 amps. 12 ga wire is good for 19 amps so you don't need anything else to allow you to do this.
John from Baltimore "One Day at a Time" All replies based on the 2008 NEC Quote:
So according to that I could use a 30 amp breaker on #12 also. Since the 175% short circuit protection would still be meet.
Or in this case since the nameplate states 30 amp breaker is ok. |
Philadelphia electrician
Trade: Electrical contractor
confusing, no?
I had problems with this for a while, but the breaker only provides short-circuit and ground fault protection. The overload protection is inherent in the AC unit http://www.mikeholt.com/code_forum/s...earchid=182725 http://www.mikeholt.com/code_forum/s...ing+protection |
Service & Repairs
Trade: Electrician
You could use #14 AWG, and a 30 AMP double-pole circuit breaker and meet code in this situtation.
440.6 Table 310.16 240.4 (D) 240.4 (G) 110.3 (B) But in my opinion, and if this were my job (and I have done hundreds of these split-system installs), I would use #12 AWG and use a 25 AMP double-pole overcurrent protection device. |
| Has anyone used PROBLAST equipment. | jeryst | Tools & Equipment | 17 | 12-03-2011 09:53 AM |
| Used equipment... | mattbatson | Excavation & Site Work | 18 | 10-06-2007 06:48 PM |
| Single-phasing, surge arrestors, and HVAC | Beren | Electrical | 6 | 08-08-2007 05:37 PM |
| Commercial HVAC Reading Material | TheRyeCatcher | HVAC | 3 | 07-26-2007 08:50 PM |
| Sound Proofing HVAC Equipment | hoek | HVAC | 1 | 10-05-2005 10:42 AM |