Trade: C-10 Electrical Contractor
600A Service...Long Pull!
I have a 120/240 404A load (600A srvc), a 600ft distance (sloped), and (3) 200A subs. If my calcs are right, w/500 mcm, my drop should be around 2.8v. Does that look right? Thanks everyone, I learn more here at this forum than I do in the "Crapper". MAC
Fentoozler
Re: 600A Service...Long Pull!
Service & Repairs
Trade: Electrician
Celtic, will he need to use 300 (285 amps) or 350 (310 amps) kcmil, in parallel, assuming he's using equipment rated for 75º?
Does 240.4(B) permit using 300 kcmil for this job? |
Fentoozler
You could use the 300's (CU)...and the allowance of 240.4(B) for the 600A service....this is, of course, provided the calculated load is under 570A.
The OP could even use 250's...as long as the calculated load is under 510A. This would be a risky proposition...even though the OP has stated the load is calculated at 404A - things change...and I would be plenty PO'ed at paying for 600A and only getting 510A capacity should the need arise for that 90A paid for once already. (All of the above is taking no notice of any VD)
Service & Repairs
Trade: Electrician
Thanks for the info. And I agree, I would want a true 600 amp service if I was paying for it. So if you consider the 12.5% voltage drop (5.2 VAC) he would likely need to use the 350's for a true 600 amp, no?
Fentoozler
More than likely....but not having done the math (on account of SEVERE laziness due to multiple bowls of pasta fagioli)...I guess so
Glad I could help massage your ego Celtic...and by the way it was "Linguini w/Two Sick & Screaming Bambinos" CAPICHE?!
Yeah I was being lazy, should have blown the dust off the old "On-Line Volt Drop Calculator"...thanks for that link by the way. Fact of the matter is guys is I have not been doing this for a very long time and I do have a lot to learn, but you can make sure that I am going to do my homework before I start making 50 or 100k mistakes. MACYour feedback has been "gratiously appriciated" |
| Service Magic, good or bad? | cowtown | Online Leads Services | 21 | 08-10-2009 02:07 PM |
| Difference between new work and service | mdshunk | Business | 2 | 09-09-2007 01:19 PM |
| Advice on Answering Service | BrianS | General Discussion | 7 | 06-07-2007 11:24 PM |
| Setting up service department | pcisam | General Discussion | 0 | 04-27-2007 09:38 AM |
| Roofer vs. Roofer (Just a long winded hypothetical) | Thunder1 | Roofing | 7 | 12-01-2005 10:22 PM |