Tricks To Sizing A Heat Pump
Old 06-28-2007, 12:20 PM   #1
Danno6102's Avatar
Trade: Deck Builder
I am looking at buying a heat pump & having a friend finish the install in my personal home that I havebeen gutting & remodeling between jobs. I've done the manual J & D calcs. Says I have a heat gain of 25,911 (2 ton) btuh & heat loss of 46,154 btuh. What size heat pump would be needed to meet these values? Also, what size electric element would I need in the air handler?
Thanks!
Dan
Danno6102 is offline
Old 06-28-2007, 06:05 PM   #2
mdshunk's Avatar
Re: Tricks To Sizing A Heat Pump
Size for the cooling load only, and add enough electric heat to do the heating side if need be. In your case, that's 13kw, so you'd probably go with a 15kw heat kit.
Resist the urge to upsize the heat pump itself for the heating load, because it will be way oversized in the summer, according to your calcs. The temperature setpoint will be reached way before any dehumidification has been done, and the place will feel like a cold, clammy, damp basement.
mdshunk is offline
Run a Heat Pump on solar power SR Martin HVAC 173 11-20-2010 12:38 PM
heat pump help!?!!! maxkd HVAC 1 11-10-2006 08:57 PM
Forced Air Furnace w/Air Heat Pump Backup mahleumon HVAC 1 03-14-2006 10:15 PM
heat pump chuck79 HVAC 0 01-26-2006 07:04 PM
Heat Exchanger Inspection Methods MechAcc HVAC 3 04-14-2005 04:38 PM