How Can I Be Sure I Am Getting The Correct The CFM Draw From Rooms Served?
Old 04-02-2009, 01:24 PM   #1
JimmyH's Avatar
I have a completed town house project where I need to establish that 2 baths and kitchen are properly vented from a 100 cfm fantech in line exhaust fan.
I should have the 65 cfm required for continuous operation however mirrors continue to fog over and kitchen air is not moved (smokes activate) to our satisfaction.
Arguing with the engineer is no good because the math works, but in practice the system doesn't.
Is there a simple test at 20 - 25 cfm that can be done with minimal expense?
JimmyH is offline
Old 04-02-2009, 08:49 PM   #2
MechAcc's Avatar
Trade: HVAC Service Technician --RSES CM-- NATE Certifie
Re: How Can I Be Sure I Am Getting The Correct The CFM Draw From Rooms Served?
One thing to remember about venting air out of a structure, air must come in to replace that air. Nature abhors a vacuum. If this is a newer structure and is well sealed it may have trouble bringing in fresh air. A makeup air system may need to be installed or a energy recovery ventilator installed and adjusted to run the building slight positive pressure.
MechAcc is offline
Old 04-03-2009, 03:12 AM   #3
consolidatedbui's Avatar
Well i dont think a bath fan is going to fault cause no outside air... Personally, in theory yes, but the house does leak a little..
use a volumeter????????????
consolidatedbui is offline
Old 04-03-2009, 08:06 AM   #4
NICKTECH
NickTech's Avatar
Send a message via AIM to NickTech Send a message via MSN to NickTech
quick smoke test to disprove negative pressure. with the fan off create some smoke(ie cigarette, or use fine talcum powder) ensuring any windows are closed, then energize the fan and observe smoke draw. now repeat process with a window open and observe the draw. note any differences and conclude a solution.
this is now assuming there are no install problems like closed dampers or crushed duct and thee aren't any obstructions outside.
goodluck
NickTech is offline
Old 04-03-2009, 09:52 AM   #5
flashheatingand's Avatar
Trade: H.v.a.c.
You checked the ducting and the fan operation? and you aren't getting enough air flow?
Disconnect the intake side of the fan and disconnect the output ducting of the fan, then energize it and do the smoke-test thing. Does it appear to be working ok? Step 2 reset the intake duct and check the airflow (smoke test)is it still ok?. If so, your problem is likely on the output side of the fan.
Before calling out the engineer, I would isolate the components to verify that my stuff is good.
flashheatingand is offline
Old 04-09-2009, 08:13 AM   #6
coolmen's Avatar
Trade: hvac
65 cfm for 2 bath and a kitchen does not sound like much if you ask me.
coolmen is offline
Old 04-12-2009, 09:51 AM   #7
beenthere's Avatar
Trade: HVAC
Code generally requires 25CFM per bathroom fan, if they are wired fo continuous 24/7 run.
So that would be 50CFM for 2 bathrooms.
15 CFM for a kithen isn't enough.
beenthere is offline
Looking for basic software to draw floor plans and elevations JBowman Drafting & CAD Forum 10 11-27-2011 04:54 PM
Construction Draw Schedule VBuilt File Swap 9 01-09-2010 09:05 PM
Biscuit and glue correct deck? PA woodbutcher Decks & Fencing 13 12-04-2008 12:50 PM
correct deck ghayes Decks & Fencing 8 08-25-2008 08:46 AM
Somebody sell some Gass Rooms Glasshousebltr Construction 2 03-04-2004 10:46 AM