Hot Air Furnace Will Not Shut Off
Old 02-08-2011, 04:01 PM   #1
mrmike's Avatar
Trade: Electrical & Carpentry
Should not have got into it-but I did-Furnace in a dirt crawl space with no room to work. I was there for another "electrical" job & the customer said that she had a unit that the furnace would not shut off & it was over a hundred in the place.
First I unhooked the T-stat to no avail. Went in the crawl space & unhooked the wires from the T-stat-still running. Shut it off with the breaker.
Found the Honeywell Control circuit board with a couple of burnt resistors on it. Ok theres the problem. Went out & got a replacement board Honeywell ST9103A1002 & changed it out. The Blower fan starts first & 30 to 45 sec later the Burner...... Stat satisfied still won't shut down-unhooked stat wires again with same- Whats up?
Isn't the Blower supposed to start after the Burner? I checked my wiring over & over & everything seems right.. Any Thoughts ??? Thanks in Advance...........
mrmike is offline
Old 02-08-2011, 08:57 PM   #2
flashheatingand's Avatar
Trade: H.v.a.c.
Rewards Points: 3,466
Re: Hot Air Furnace Will Not Shut Off
Does the blower stay on all the time or do the burners stay on all the time?
flashheatingand is offline
Old 02-09-2011, 05:12 AM   #3
mrmike's Avatar
Both stay on until I cut the power........I have to figure out why the limits don't open up & shut it down.. Any ideas?
mrmike is offline
Old 02-09-2011, 08:08 AM   #4
Trade: H.v.a.c.
The limits shut it down if the furnace overheats, its not a bad thing if the furnace can run indefinitely.
Old 02-09-2011, 08:12 AM   #5
Trade: H.v.a.c.
But clearly somehow something is wired wrong. There should be a wiring diagram on the back of one of the panels. I wish I could be of more help, but it sounds like something one has to be present.
Old 02-09-2011, 11:29 AM   #6
BigReds's Avatar
Trade: General Contracting / Handyman
Rewards Points: 75
theres a relay thats sticking
BigReds is offline
Old 02-13-2011, 02:41 PM   #7
OT Ready's Avatar
Trade: HVAC
Disconnect stat wires at furnace to eliminate field installed control. If problem persists, you know it is in the furnace control. (I.E. stuck relay.)
May be a shorted stat wire.
OT Ready is offline
Old 02-23-2011, 06:36 PM   #8
Dr Heat
Dr Heat's Avatar
Trade: hvac
Rewards Points: 306
make? model? Fuel type?
Dr Heat is offline
Fresh air duct work for oil furnace 3Rivers HVAC 14 12-07-2010 05:27 PM
Outside roof furnace noise/hot nicmac HVAC 2 09-23-2010 10:06 PM
Oil furnace blowing cold air batzld HVAC 4 03-28-2010 03:30 PM
Direct vent furnace draft inducer ArmstrCarpentry HVAC 4 07-26-2009 11:45 AM
Energy Tax Credit AC and/or furnace? Warren HVAC 3 07-02-2009 09:26 PM