Actually that isn't a bad temperature, rather usual for oil burner heaters over decades, one reason for having oil burner venting different from gas venting. However, many do run at lower temperatures.
It's a bit difficult to analyze from here, but some things to consider are:
1. Are all parts and nozzle the same as in the Burnham catalog that the boiler was tested with at the factory? The 60A Delavan nozzles are shown in page 96 Table 6 of the catalog:
http://www.burnham.com/PDF/V8_I&O.pdf
2. Is a small nozzle baffle required for that burner?
3. Is the pressure at 140?
It is possible the flame is being drawn through the heat exchanger to the breech faster than heat can be absorbed due to the power vent and burner part settings, so further adjustment of the head and draft might be necessary.