Go Back   Contractor Talk - Professional Construction and Remodeling Forum > Trade Talk > HVAC
Old 06-24-2009, 10:08 AM   #1
Trade: HVAC Residential Commercial
Heat Pump Condenser coils going bad
Have any of you guys ever had this happen? The first time it happened it took four years to get to the point of failure. All the refrigerant and oil leaked out and the compressor seized. The manufacturer wouldn't give me a new unit so I had to rebuild the old one. They gave me a new coil and compressor. After just one year, it happened again. The original installer didn't use pump ups so I put them on when I rebuilt the unit. This is a heat pump installed in northern Pennsylvania. I'm at a loss to explain this and so is the manufacturer.
DCHVAC is offline   Reply With Quote
Old 06-24-2009, 08:25 PM   #2
HVAC Tech, NATE certified
Trade: Hvac technician. Economy Heating, Pittsbur
who else tried to wipe that hair off the screen?
Best line from a customer "you here for the tune-up? the tank of 22 is in the shed, let me know if you need more."
Verbal is offline   Reply With Quote
Old 06-26-2009, 08:10 AM   #3
Trade: HVAC Contractor
Definitely from ice build up. Might not be high enough off of the ground, defrost time too short, charge low or unit is located on the eave side of the home. Just some suggestions.
westernhvac is offline   Reply With Quote
Old 07-08-2009, 08:25 PM   #4
Thanks
Thanks for the reply Western. I thought it was from snow since it was only the first loop of the coil but the home owner is insistent that snow never builds up where the condenser is. I thought about the defrost issue as well but wouldn't the entire coil have the same damage if the defrost was the issue? I've observed many HP condensers just before they go into defrost and they all have frost building in bands all around the coil and not just on the first loop on the bottom. This is where I'm stumped.
Old 07-08-2009, 08:32 PM   #5
manager
Trade: heating cooling tech
Looks like you have a dog peeing on the coil. Have seen it take the bottom of the coils out.
greghvacguy is offline   Reply With Quote
Old 07-09-2009, 10:13 PM   #6
Trade: HVAC
What is the scrap mark on the coil from a screwdriver? How high is the damage 1.5"? First two tubes.
The Veto toolbag, the Louis Viton of tool transport. The official toolbag of rich guys.
BigMikeB is offline   Reply With Quote
Old 07-11-2009, 03:36 AM   #7
Yes BM, the first two tubes. The damage is from fin deformation and then copper failure after that.