Goodman HP Start Up Issue - HVAC - Contractor Talk
Old 01-22-2015, 01:21 PM   #1
OLD's Avatar
Trade: refrigeration
Rewards Points: 8
5 ton goodman heat pump split system w/ matching AH, 1 phase, r-410a
My neighbor bought two 5 ton split systems and asked me to install.
I connected the line sets, pressure tested, evacuated, added additional charge to line sets ( on liquid side only) according to mfg reccomendations, opened service valves, energized and allowed crankcase heaters to operate for three days before start-up.
ON startup the low and high side pressures were same as static.
I checked the solenoid on the reversing valve and it does click when energized. There is voltage to the rv sol valve in cooling mode.
I thought it might be the floating seal in top of the scroll comp. so I recovered the refrig , pulled system into vac and then recharged the liquid side with only about 5 lbs of refrig.
Stil have equal pressures when system is started in cooling mode.
I don't normally install or work on residential equip and have little experience with heat pumps.
any thoughts would be greatly appreciated.
OLD is offline
Old 01-23-2015, 05:37 AM   #2
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,126
Re: Goodman HP Start Up Issue
Is/are the compressors actually running.
beenthere is offline
The Following User Says Thank You to beenthere For This Useful Post:
flashheatingand (01-23-2015)
Old 01-23-2015, 01:45 PM   #3
OLD's Avatar
Rewards Points: 8
compressors do run, pull about 10.5 amps
OLD is offline
Old 01-23-2015, 05:06 PM   #4
beenthere's Avatar
Trade: HVAC
If a scroll is running backwards. it makes a real loud ruckus. So if no loud Ruckus, its not running backwards.
Check that RV's haven't been replaced already. Possible they were replaced and over heated.
Old 01-23-2015, 07:08 PM   #5
flashheatingand's Avatar
Trade: H.v.a.c.
Rewards Points: 3,492
Perhaps a silly question. But, you did make sure that both guage valves were closed? It's been known to happen.
http://www.37flash.com/
flashheatingand is offline
Old 01-23-2015, 07:53 PM   #6
OLD's Avatar
Rewards Points: 8
yes, both gages are closed.
I removed C.U. fan today and checked temps at RV.
106f at comp discharge, about the same at common suction of RV that is connected to accumulator and then to suction of comp, about 65 at suction line coming from inside evap coil. the RV coil does have 27v, and the coil is energized as verified by placing a screwdriver next to the coil.
I am pretty sure I have isolated the problem.
The local goodman wholesaler is bringing in a new REV under warranty.
What do you think??
OLD is offline
Old 01-23-2015, 09:15 PM   #7
Trade: H.v.a.c.
Gotta do something. Be careful not to overheat the rv when replacing. I "re-plumbed" the botom half piping so as to braze the couplings away from the valve, and brazed the tight stuff outside of the h/p.
I think I had overheated the stuff before, and there is a small tube, that breaks off easily. I think it was due to overheating, afterall.
Old 01-24-2015, 12:29 AM   #8
beenthere's Avatar
Trade: HVAC
LOL. I've done that a time or 2.
Yeah, the pilot line provides the high pressure that pushes the cylinder over can get brittle from too much heat.
Old 01-24-2015, 10:29 AM   #9
Trade: H.v.a.c.
Everything was fine, then about a year later, no heat/cool, too find the pilot tube loose
Old 02-03-2015, 08:59 PM   #10
OLD's Avatar
Rewards Points: 8
I replaced the RV on one unit. leak checked, evaced and performed rate of rise, All OK. Charged system on liquid side to Mfg specs.
Performed start-up in heat mode.
the true suction pressure was about 105 and steady. the High side pressure on the liquid line (coming back from inside coil) started about 150 and continued to rise to 500. Outside temp= 57f. t-stat set point= 75. starting inside temp at return about 60f.
Question is: If air flow is correct and all system components are working properly, is 500 psig too high? More general Q is: what would be expected high side pressure with outdoor at 57f and indoor return temp at say 74 f, just before t-stat would shut off?
I know you will all want more measurements and readings. But, a better understanding of expected pressures in heat mode would give me a better starting point to understand the heat pump w/r-410a systems.
thanks in advance for your replies
OLD is offline
Old 02-03-2015, 09:19 PM   #11
beenthere's Avatar
Trade: HVAC
Your about 50 PSIG higher then I would normally expect for a 60 Indoor temp.
Old 02-04-2015, 07:42 AM   #12
fitter's Avatar
Trade: hvac
Rewards Points: 33
There should be a charging chart attached to the c.u. panel.
fitter is offline
Old 02-04-2015, 09:15 AM   #13
Trade: H.v.a.c.
Did you weigh in the charge? Factory charge, which you probably know is for 15ft of lineset, and .4 ounces per ft. after.
Old 05-19-2016, 11:50 PM   #14
JT1990's Avatar
Trade: c20-c38 HVACR
Rewards Points: 12
ive had a similar situtation when i first got in the trade.
split 3 ton.
replaced the CU but left the AH.
brazed in the line set , the service ports on the CU ( allen head wrench type ) were front seated all the way, and we assumed that stood for open.
long story short, charged it with 22, ran and the comp sounded okay, but nothings working, pressures same. finally we realized oh crap the valves man.
lol and that comp is running fine and chippy.
JT1990 is offline
Old 07-27-2016, 12:53 AM   #15
texarkanahvac's Avatar
Trade: HVAC
Rewards Points: 54
Check the valves! They sneak up on you
texarkanahvac is offline